View Full Version : mitsubishi auto restart
philjd26
13-01-2009, 06:47 PM
hi
two mitsu electric splits connected too one controller, what dips do i hit to enable auto restart???
rgrds phil
marc5180
13-01-2009, 08:45 PM
Hi Phil, if i remember correctly im sure it is sw1 dip sw 9 on indoor units or pull the controller apart and check dip switch SW3 inside the controller. Should be in on position for auto restart.
Thermatech
13-01-2009, 11:10 PM
If the units are Mr Slim R410a models
Outdoor unit model PUHZ RP_ _ _
then
Power failure auto restart can be set at outdoor unit SW5 No2
or
Remote controller engineer mode fuction mode 01 setting No2
philjd26
13-01-2009, 11:30 PM
thanks for reply lads lads, its old enough 407c maybe late 90s...
rgrds phil
vBulletin® v3.7.4, Copyright ©2000-2009, Jelsoft Enterprises Ltd.