11-01-2009, 10:30 PM
hey ive got a mitsi condenser pury-p250ygm-a and 5 indoors plfy p63vame. the original set up was 2 of the units had being in a office and now they have split them up. i went and added a additional remote control to the unit in the new office and wired it correctly and addressed the remote. all was working fine and dandy untill i got a call out to the client the units will not controll individually. i can only run both units when the new remote is turned on, any ideas ?

Brian_UK
11-01-2009, 11:23 PM
Double/triple check all of the unit addresses, system settings and wiring connections.

Thermatech
11-01-2009, 11:23 PM
This is not daikin system

Just because you connected the remote control to the indoor unit & set address it will not control only that indoor unit

&

other remote controls which were set to contol a group of indoor units will not change to individual contol unless you change address & group control settings

Please advise address settings for all units & remote controllers & also which units need to have individual control & which units need group control

first you need to understand basic mitsubishi address setting logic

then

you can make new address settings which will work

then

you can set correct address settings & carry out virgin restart

then all unit will work as you require