08-01-2009, 05:01 PM
hi chaps,merry new year!!!!!
back to it....
i am trouble starting a pury-p250ymf-b.first of all this unit had aleak which i repaired. started sytem up, and went into warm up mode(2xphases to comp)tripped on an error 4210 i think, something to do with inverter...anyway i discovered that the compressor was mechanically seized which was throwing the error up.
I went to check the diodes n transistors which checked out ok.
Put everything back together and thought i would check across the phases for balance, which many of you recommend.
so before turning power on i decided i would do a virgin restart to clear errror record.Turned power back on and now nothing is starting....
at start up on the outdoor LED i get 51 which is outdoor address followed by segment 2 and 8 flagged... nothing after that, inverter does not try and start and no errors on controller any ideas??
rgrds phil
back to it....
i am trouble starting a pury-p250ymf-b.first of all this unit had aleak which i repaired. started sytem up, and went into warm up mode(2xphases to comp)tripped on an error 4210 i think, something to do with inverter...anyway i discovered that the compressor was mechanically seized which was throwing the error up.
I went to check the diodes n transistors which checked out ok.
Put everything back together and thought i would check across the phases for balance, which many of you recommend.
so before turning power on i decided i would do a virgin restart to clear errror record.Turned power back on and now nothing is starting....
at start up on the outdoor LED i get 51 which is outdoor address followed by segment 2 and 8 flagged... nothing after that, inverter does not try and start and no errors on controller any ideas??
rgrds phil