PDA

View Full Version : Honeywell/Elm Dialout testing


Latte
16-03-2004, 12:42 AM
Hi All,
Anyone out there know how to check to dial out operation on a Honeywell/Elm system (PC Visor or Supervisor 64)

Thanks

Raymond

Mark
16-03-2004, 01:10 AM
Hi raymond:)
Supervisor 64 or touchscreen via service mode.
From service menu press 3
The screen lists the different alarms on the left ,while on the right is the selected dialout action -none,night,day or always.
IE NONE the alarm is not urgent

NIGHT Dial the alarm centre if this alarm occurs at night.

DAY Dial the alarm centre if this alarm occurs during the day

ALWAYS Dial the alarm centre whenever this alarm occurs.

However to test dial out during trading hours or when you are in the store,Depending on dial out config say its set to night dial out set it to always and simulate a alarm o/t or u/t probe fault etc and ring alarm centre to confirm alarm has been recieved.
Or if set to night adjust real time (on top end) forward so simulating out of hours or (night)ie if 13:00 hrs dial out set to 22:00 set real time to 22:05 etc.Then simulate an alarm wait for dial out ring alarm centre for confirmation of alarm.
Hope this helps ray

Kind Regards Mark:)

Latte
16-03-2004, 01:12 AM
Cheers Mark,
Another one of Merv's CAN YOU JUST POP IN AND jobs

Regards

Raymond

Latte
16-03-2004, 01:21 AM
Will give it a try tommorow, just got in been out since 21:00
Power cut in biggleswade & all "S" comps gone out on overloads.

Really as i am on call this week i should be making sure they DONT phone out :D

Regards

Raymond