Hi friends...one question is bothering me from a very long time...CAN WE CHARGE OUR REFRIGERATION SYSTEM (compressor, condenser, Evaporator and refrigerant control device: i mean complete system) with 400psg. N2 or dry air pressure for leak testing purpose is this is advisable or not ??

nike123
29-11-2008, 10:33 AM
Hi friends...one question is bothering me from a very long time...CAN WE CHARGE OUR REFRIGERATION SYSTEM (compressor, condenser, Evaporator and refrigerant control device: i mean complete system) with 400psg. N2 or dry air pressure for leak testing purpose is this is advisable or not ??
Do not introduce any type of air in refrigeration system. Rest of answer is in other thread.
There is no need to start multiple threads to get more quicker answers!:(

boy
01-12-2008, 03:36 PM
pramoddhiman,

what a name,anyway dry nitrogen is recomended for leak testing and a 200 psi pressure that stands for 24 hours is sufficient.a 400 psi pressure is too much and may burst a type M copper pipe as i have seen before.

regards,

martinw58
02-12-2008, 09:01 AM
the tests pressure depends on gas used and max pressure of parts fitted