HI All,
I have problem to solved TK CSR40 microPD unit (reefer container ) which has cooling down problem.
These parts have been replace ( TXV, LIV coil, clean up system, recharge refrigerant ) Problem hasn't solved yet.

Please help

Brgds
Teguh

reefer
06-12-2008, 12:10 PM
re evap. fans running right direction.
reefer

reefer
06-12-2008, 12:11 PM
have you checked for alarm codes
does unit complete full auto PTI
reefer

Will
07-12-2008, 03:47 PM
Why were those parts replaced ?, did they test bad ?

What is your modulation valve doing ?

And like Reefer said, does it pass PT ?

I'm ASSuming it won't, so at what mode does it fail in and what alarms do you receive ?

Head pressure ?
Suction pressure ?
DT temp ?
Super heat reading ?

teguh
09-12-2008, 04:31 AM
Hi Will and reefer,
Thank for your reply.
The evap motors are run right direction. No alarm appear during PTI, but temp goes down too slowly while precool step.

The problem has been solved. It was caused by microprocessor failure.


B Rgds