Quick one. Has anyone see 99 come up on an Eliwell controller. We have tried changing from PTC to NTC no change. Controller damaged?

Chunk
26-11-2008, 06:54 PM
What happens when the probe is disconnected,does it show a probe fault or just stay at 99?

Grizzly
26-11-2008, 09:45 PM
Basic I know but have you tried powering down and then powering back up?
Just to confirm you don't just have a confused display.
Pretty much what chunk is suggesting!
Grizzly

Grizzly
27-11-2008, 07:15 AM
Fuair.
Please read the bottom line of the attached useful Eliwell Controller instructions.
Grizzly

Grizzly
27-11-2008, 08:38 PM
Frosties

Quick one. Has anyone see 99 come up on an Eliwell controller. We have tried changing from PTC to NTC no change. Controller damaged?

Back again, it is just possible that you have the keyboard LOC on as you can still access the programming mode via the set button.
whilst viewing the set point. Which incidentally has a maximum value of 99 (sound familiar).
Please read the attached info and hopefully all just may be revealed? (see bottom L/H of first paragraph)
Grizzly

Alan Twomlow
02-04-2009, 11:39 AM
This problem occurs when the controller is expecting to see one type of sensor input (i.e. NTC) and another is connected (i.e PTC). You can change the probe input type in folder CnF, parameter H00 but you MUST then power down the controller and then restart it, otherwise it will not accept the new probe input. It's simple when you know how.

Grizzly
02-04-2009, 09:25 PM
This problem occurs when the controller is expecting to see one type of sensor input (i.e. NTC) and another is connected (i.e PTC). You can change the probe input type in folder CnF, parameter H00 but you MUST then power down the controller and then restart it, otherwise it will not accept the new probe input. It's simple when you know how.


Welcome to the forum Alan.

You are obviously a well informed Engineer?
I am sure there will be more questions of you!
Grizzly

Brian_UK
02-04-2009, 11:03 PM
Ditto that, welcome to the forum Alan, we hope that you enjoy it.

LRAC
03-04-2009, 07:38 AM
Only took him 8 years for his first post, see you again Alan in 2017.

Alan Twomlow
03-04-2009, 02:02 PM
Only took him 8 years for his first post, see you again Alan in 2017.