I am new to air conditioning and this forum,

been a plumber and electrician for a long time now, moved over to Spain (from UK) 3 years ago, my only AC experience is fitting about a dozen split units, dakin, hitachi, verhal, nothing complicated.


so to my beginners questions

1st brazing
this is embarrassing as a plumber, but i have never braised, though with over 25 years in the trade i have seen my share, I will only be working on domestic units with a max 5/8" pipe
Do you use flux?
I assume you clean the joint prior to brazing?
I have only seen you use ex panders to make the joints, I cant find ex panders for 1/4" pipe?
can you use pre made joints?
I have seen locally (only on 1/4")just map gas being used, I had always assumed you needed a small oxy kit to braise?


How do i determine if there is enough gas in the unit?
not new units, pre installed units, I had a leak on a unit, not a joint but a duff o'ring on a gauge hose, I had no idea how much gas had been lost so i just added more gas until it started working properly (here's you all cringe)
I have bought 3 books on AC/Refrigeration but none give any real info on this (for a modern split unit)

any info on this would be appreciated, maybe a good book recommendation

thx
Steve

marc5180
17-11-2008, 06:32 PM
Hi Steve,

1) Flux isn't needed when braizing copper to copper pipe, i only use it when trying to braize copper to brass or things like that.

2) You can buy a little kit that expands 1/4 but i tend to use the 1/4 sockets, much quicker in my opinion.

3) Mapp gas will work fine on braized joints up to 7/8th if you have the double ender then you can go up to 1 1/8th.

4) To determine if there is enough gas in a unit, you need to take temperatures at different points around the system and work out your subcooling and superheat. Just topping a sytem up will reduce efficency, as more than likely you will have added more gas than necessary and if that is the case then you will be filling up the bottom of the condensor with overcharge thus reducing the capacity of the sytem.

Edit... Also with regards to a good book, a friend of mine has just got two books from amazon that he reccomended;
Air Conditioning and Refrigeration Repair and Arco Air Conditioning & Refrigeration Toolbox Manual

Brian_UK
17-11-2008, 06:42 PM
Add to Marc's no.1 , You must have oxygen free nitrogen flowing through the pipework to prevent oxidization within the pipe.

As regards 'how much to add?', do a search here on 'Superheat' and 'sub-cooling'. That will get you started,

You should perhaps be getting a Refrigerant Safe Handling ticket if they operate one in Spain - they should because it is EU regulations.

steve_k
17-11-2008, 07:23 PM
You should perhaps be getting a Refrigerant Safe Handling ticket if they operate one in Spain - they should because it is EU regulations.

they have very strict rules and very lax enforcement, so you get some very bad
practices, I fitted the first unit because the
original fitter
didn't use (
didn't own) a vac pump,
kinked the pipe 3 times (
didn't have any benders either) in a 3 m run, and all the gas leaked out anyway :eek:

You must have oxygen free nitrogen flowing through the pipework to prevent oxidization within the pipe


obviously i have seen this in the
UK, but here in
Spain on domestic nobody flushes the system with nitrogen, on 2/3m
installations how important is it?



Mapp gas will work fine on
brazed joints up to 7/8th if you have the double
ender then you can go up to 1 1/8th. whats a double
ender?

frank
17-11-2008, 08:05 PM
whats a double ender?

Excuse ME!!

This is a refrigeration forum - not a SEX forum :eek::D:D:p

Brian_UK
17-11-2008, 08:12 PM
Well, there's a difficult post to read, however...

Without nitrogen flowing the inside of the pipe will oxidize. When the system runs the oxides will wash off the pipe into the compressor where they will break down the oil and cause acid.

The acid will then attack the motor windings until it shorts out.

If it fails during warranty and the manufacturer checks to find oxides then the warranty is void.

A double ender is a brazing torch with two nozzles.

Brian_UK
17-11-2008, 08:13 PM
Nice one Frank ;)

Brian_UK
17-11-2008, 08:20 PM
Also, Steve, have a look at this thread from earlier....

http://www.refrigeration-engineer.com/forums/showthread.php?t=13832

steve_k
17-11-2008, 09:05 PM
thx for the quick replies

don't know what happened with my above post, very strange

your previous thread link was very informative thx

plenty of info on this forum will be spending some time reading over old posts

steve_k
18-11-2008, 02:16 PM
After Brian_UKs recommendation i have today purchased a nitrogen set, here in Spain you have to purchase your first bottle, then just pay for the refills, the bottle cost 580e and the refills are 35e (11ltr) how does that compare to the UK?

so I have my nitrogen what do i do with it?
flushing how much do i push through the new pipework?
pressure testing, what pressure do you fill to? how long do you leave under pressure?
vacking, i presume i have to vack the nitrogen out of the pipe before gassing up

All this sounds very amateurish, and you may be thinking that i have no business fitting AC units, I have over 25 years in the trade (plumbing and electrical) I have 95% of the skills required, I only intend to fit domestic precharged split units, I have no intention of calling myself or becoming a service engineer, I just need to put in good practices to ensure my fitting has no detrimental effect on the unit, 4 compression fittings on 3m of pipework is hardly rocket science, with a bit more patience and guidance you may help me become more competent

Steve

nike123
18-11-2008, 03:05 PM
This is article for arc welding of steel tubes, but could be considered also for copper tube brazing and nitrogen purging:
http://files.aws.org/wj/2006/12/wj200612/wj1206-38.pdf

Brian_UK
18-11-2008, 07:56 PM
Pricing in the UK..

We pay about 76Euro for a 10l bottle which includes the bottle deposit; sorry no idea how much the gas is.

Electrocoolman
18-11-2008, 09:08 PM
Steve....Nitrogen set?...presume (hope) you are referring to pressure regulator?

You will in fact need two different pressure regulators....one low pressure (150 psi) which will allow you two get a small psi for small flow whilst brazing.
The other one will be high pressure (500 psi) which you need for pressure testing on modern R410 systems.

Under NO circumstances do you connect nitrogen cylinder directly to system without regulator.

steve_k
18-11-2008, 11:49 PM
Steve....Nitrogen set?...presume (hope) you are referring to pressure regulator?


Under NO circumstances do you connect nitrogen cylinder directly to system without regulator.

lol see I am coming across as an armature, not ac or plumbing related, but i am a scuba diving instructor, and i have a gas blending ticket o2 and helium to 300 bar

back on topic
yes I purchased a regulator, it has 2 gauges for the cylinder and secondary pressure, and it looks like i can set the secondary from 0 to 45bar


you say

Under NO circumstances do you connect nitrogen cylinder directly to system without regulatorout of interest what is the working/test/fail pressure of refrigerant copper pipe?

steve_k
18-11-2008, 11:56 PM
electrocoolman
you are from the UK and you are using psi, is this standard for the trade? i thought it was just the Americans using psi nowadays, maybe its just my scuba training.

nike123
19-11-2008, 12:00 AM
yes I purchased a regulator, it has 2 gauges for the cylinder and secondary pressure, and it looks like i can set the secondary from 0 to 45bar


That is pressure regulator for pressure test with nitrogen and for blowing.
For air purging you need pressure regulator with flow regulation!
That mean you need two regulators!;)

steve_k
19-11-2008, 12:15 AM
OK back to my diving background, if on my rebreather (yes another ticket i have) if i don't have my flow rate correct i die, its that simple.
back to ac, whats wrong with cranking open the regulator a bit to flush the system? we are talking about flushing out the o2, how accurate do you think the flow rate needs to be?

please remember i am doing small runs of un brazed pipework

nike123
19-11-2008, 12:23 AM
OK back to my diving background, if on my rebreather (yes another ticket i have) if i don't have my flow rate correct i die, its that simple.
back to ac, whats wrong with cranking open the regulator a bit to flush the system? we are talking about flushing out the o2, how accurate do you think the flow rate needs to be?

please remember i am doing small runs of un brazed pipework

After flashing 0.2-0.4 l/min.

steve_k
19-11-2008, 12:31 AM
After flashing 0.2-0.4 l/min.

I have no idea what you
are on about, do you mean
flushing?

paul_h
19-11-2008, 07:23 AM
When brazing they are saying you need a regulator that has very fine control, feeding a certain flow rate into the system while brazing with a low pressure regulator, rather than using a high pressure regulator which is just for pressure testing as you can't set them to an accurate low flow rate.
Pressure testing disconnected pipework should be done to at least 2000kPa, as the units run themselves at 3500kpa when on heating.
2000kPa is the minimum, I normally pressure test to the whole 3500kPa if I suspect a leak.
When pressurizing a assembled unit though, standing pressure across the valves is usually only 800kPa, so if you go over that limit, you run the chance of your nitrogen getting past a leaking valve and ruining the precharged gass.
Search for threads here about that possiblity, as it's already been discussed.

If you are just going to be split bashing, odds are you won't be brazing that much and you can just use your service gauges to limit flow IMHO.
It's mainly in repair you need to do a lot of brazing (replacing components, repairing leaks etc)
But if you have to supply warranty to your own unit's, you may need to repair and be more qualified.

nike123
19-11-2008, 07:44 AM
I have no idea what you
are
on about, do you mean
flushing
?
Sorry for mistyping.
With flushing I mean prepurging process to lower O2 amount in pipes to acceptable level. For that, you need to adjust flow to 20l/min for some time depending on pipe diameter end length. When flushing (prepurging) is done, you need to reduce flow to 2-4l/min (I was wrongly said in previous post 0,2-0,4) to be able to braze without disturbing brazed joint.
For that purpose, I use Co2 regulator for MIG welding.

tony--1
19-11-2008, 08:00 AM
I know every 1 needs help . but this guy has gone out and got sumthing that could kill him with no idea how to us it . every 1 starts sum where but a little training would be good . you would not let your boy thats just left school loose with the nitrogen on a job you were on .

nike123
19-11-2008, 08:52 AM
I know every 1 needs help . but this guy has gone out and got sumthing that could kill him with no idea how to us it . every 1 starts sum where but a little training would be good . you would not let your boy thats just left school loose with the nitrogen on a job you were on .

I think that you are overprotective! He is big boy now!:)

steve_k
19-11-2008, 09:16 AM
I know every 1 needs help . but this guy has gone out and got something that could kill him with no idea how to us it . every 1 starts sum where but a little training would be good . you would not let your boy that's just left school loose with the nitrogen on a job you were on .

thx for the vote of confidence:)

I have an O2 and helium handling and blending certificate, and i can assure you that can kill you much more than nitrogen will (not sure how you could be killed more though lol)

thx for the info on prepurging

re brazing, I have had a lot of contact in my career with air conditioning, mainly commercial, I have seen hundreds of installs by different companies and have never seen nitrogen being used in conjunction with brazing, do you all use nitrogen when brazing?

Training
what training could i do? my Spanish is not good enough to go on any Spanish course, so it would be back to the UK, any hvac course is just too much for my intended use and i would never use 95% of the course content, there are some specific 4/5/7 day courses, but again 90% of the content would be telling me how to suck eggs, I had been seriously considering the gas handling certificate, but its tailored for the UK regulations and is worthless in Spain,

In my area of Spain there are lots and lots of people who fit AC (domestic) and most have no training, I only know of 2 companies that use nitrogen and they do mainy commercial, I know of more than a few that don't even have a vac pump,

I want to provide a proper service, i want to know that it is fitted correctly, I am here asking for you help because I know I have a shortfall in my Knowledge and skill base:rolleyes:

:off topic:
last week I went to quote for a central heating system, weighing all the factors up I knew that hot/cold AC split units where a much better option for the customer,
Do i just stick to the central heating to get the work?
do i tell the customer about the AC option and loose the work? or do i fit the AC?
work is much harder to come by in this area of Spain and i am finding i need to expand my services to keep me in work.

Steve

dogma
19-11-2008, 11:54 AM
Steve. If you're just planning on fitting Split system A/C units up to 14KW on a restricted A?C ticket then you will need the following tools.


R410a Flareing Block

Spring benders and Rachet type Benders For 3/8, 1/2, 5/8, 3/4, 7/8.

A vucuume Pump

A vuccustat

Scales

Digital Leak detector

Recovery Unit and Bottle

R134a/R22 Manifold Guage set

R410a Manifold guage set

Rotary Hammer drill

Turbo Tourch (mapp Gas) (cig turbo Tourch braises up to 1 1/8")

Expanders

And your basic Hand tools


... You Can buy Copper unions for 1/4" but I just use 5/16" tube and make my own unions.


....My advice to you Steve is go into your local A/C and Refrigeration wholesaler and Have a chat. Look around at what you think you might need and ask them for some advice... I don't know what it's like over there but the wholesalers are usually retired from the trade and know what they are on about.



_DOGMA-

steve_k
19-11-2008, 01:50 PM
the wholesalers speak Spanish, getting the correct size copper can be hard enough

I don't see the nitrogen bottle on your list :-)

I have all the tools apart from the recovery unit, digital leak detector, and proper scales,

not sure i would get to use the recovery unit, but again i don't know do i

Peter_1
19-11-2008, 06:55 PM
You have pressure regulators and flow regulators.
A flow regulator gives you a certain flow/minute and can't build up a pressure where a pressure regulator regulates a certain pressure.
I've done a lot of tests and we use these extensively while doing the test for the EU certification and you will need 3 to 1 bottles if you don't use a flow regulator while brazing.
They look the same but the working principle is completely different.
The smallest flow of nitrogen is enough is OK and we set it to 5 l/hour.
Make sure that where you connect the OFN or insert it in the tubes you blank it off with tape so that you don't suck air together with the OFN.http://www.aquariumlighting.com/retail/images/Milwaukee_CO2_Adjustable_Flow_Regulator.jpg

or

http://nuvair.com/shopsite_sc/store/html/media/HVR-4401.jpg

Peter_1
19-11-2008, 07:02 PM
On the outlet, you can install a small SV and control it by a small and cheap remote control so that you can stop the flow when you stop with brazing.
Saves you a lot of OFN.
Something like this.
http://www.znt-electron.com/img/product/socket/ZTC-316.jpg

dogma
19-11-2008, 10:49 PM
Thats a bloody good idea peter_1. It's such a simple solution for saving OFN.

...Sry Steve, I fogot the OFN and regulator(s). :) :)


______ Have a look at this Product Catalouge... BTW If you want to purchace any of this stuff from Australia due to the value of our dollar atm $1.00 US = 65cents Australian, send me a pm and I'll put you on to my supplier.



http://www.airzone.com.au/index.cfm?page_id=1022&page_name=RES%20Price%20Guides

Testech
20-11-2008, 08:16 AM
Good on you mate for getting out there and actually doing something...
I have just finished working for a cowboy in the UK with 15 yrs experience who still didn't have a clue.
I would write down the actual processes in fitting the units and write a small but concise training manual.
Why not try doing it right from the start ? - If you want to purge whilst brazing then that will set you apart from the others.
The internet is a great source of information, as is the install manuals for each unit.
We all know that pre-charged units are only up to a certain distance of pipe run, so if you have to add refrigerant then your going to need a good set of scales.
My advice : Do your best safely, and remember your customers are trusting you to do a good job. Never put yourself or others at risk, and NEVER be afraid to ask questions.
Good luck my friend

Testech
20-11-2008, 08:23 AM
I have just had a thought : Why not get old pieces of pipe and use them as a guide when buying copper pipe ?.
Better still get a good Spanish plumber to translate the sizes into Spanish.
Note : Rather than overfill, would everyone suggest, reclaiming, then re-charging to the correct capacity as per manufactuers instructions ?.

steve_k
20-11-2008, 10:07 AM
I have just had a thought : Why not get old pieces of pipe and use them as a guide when buying copper pipe ?.

Note : Rather than overfill, would everyone suggest, reclaiming, then re-charging to the correct capacity as per manufacturer's instructions ?.

I am just about getting buy at the merchants, I am now very good at sketches :) I have just printed out the merchants entire product page, and that has nice little pictures for me to identify what to ask for,

the reclaiming and recharging may be a good idea, I don't have a unit at the moment, would i be able to use my 410 bottle if reclaiming and recharging 410?

and thx for your positive comments, I knew i would be opening myself up for some flack admitting to my level on here,
you are right the Internet is a fantastic source of information and an invaluable learning tool

Steve

steve_k
20-11-2008, 10:10 AM
not sure what is going on with some of my posts? I back arrowed then checked and re posted changing nothing and everything is now fine?

I cant see an edit button?

nike123
20-11-2008, 12:25 PM
not sure what is going on with some of my posts? I back arrowed then checked and re posted changing nothing and everything is now fine?

I cant see an edit button?

It looks like some glossary crosslinking!
Check in user CP on Edit options that Glossary Crosslinking is unchecked and that enhanced interface is selected as Message Editor Interface

Testech
20-11-2008, 05:18 PM
What part of Spain are you in ?.

steve_k
20-11-2008, 06:09 PM
Javea
Its aproximatley halfway between Alicanti and Valencia, about 40mins north of Benidorm

icecube51
20-11-2008, 07:07 PM
Yo Steve,
i would not recommend to reclaim it together whit the fresh refrig because its blend can be wrong. it is a mix from 2 gases,and there is always 1 lighter than the other.you can keep a old bottle and remove the flow back valve,so it can be used as a recovery bottle.

Ice

cookster
20-11-2008, 07:47 PM
last time i saw pipework being purged with ofn was at college:)

Brian_UK
20-11-2008, 07:55 PM
last time i saw pipework being purged with ofn was at college:)Well, me thinks that it is time you upped your game to improve standards ;)

Electrocoolman
20-11-2008, 07:59 PM
electrocoolman
you are from the UK and you are using psi, is this standard for the trade? i thought it was just the Americans using psi nowadays, maybe its just my scuba training.

Grew up with psi.....a bar is where I go for a drink! :D

With regard to Copper sizes.....most copper used is still in imperial sizes 1/4, (5/16), 3/8, 1/2, 5/8. These are the sizes that you will come across for a/c.
You might find that metric sizes are used in spain, but the flare nuts on the a/c units are normally sized for imperial (at least in UK), so this could present you with a problem area? (i.e. leaks) (poor flare joints are one of the major areas for leaks).

Can you get pre-insulated coils of soft copper over in spain - often co-joined pairs of the two sizes i.e. 1/4 and 3/8.
You do not then need to braze, as you run a continuous length of pipe, and just flare join at each end.
Its worth investing in a decent eccentric flaring tool suitable for R410 joints. You should also invest in flare nut torque tools so joints are not overtightened.

The MG Pony
20-11-2008, 09:23 PM
Yes all ways purge while brazing any thing ells is an epic fail frankly.

One thing he didn't mention is that the oxides all so turn the oil into liquid sand paper!

frank
20-11-2008, 09:30 PM
Did someone mention BAR & DRINK?? :D

monkeydoug
20-11-2008, 10:35 PM
I applaud you for efforts Steve.

If I'm honest we only really use OFN whilst brazing on our VRV installations, this is because their can be dozens of brazes and therefore alot of potential crap in the system. For splits, especially in domestic installs, its usually only ever one or two small brazes. We use soft rolled copper in 15 or 30 metre lengths so can often have one whole pipe between indoor and outdoor, no brazes required. Also, we use MKM german copper and in 10 years have never had a problem.

We ALWAYS use OFN for a leak test, saves alot of screwing around. You should test to 1.5 times running pressure, so for R410A it is about 550 psi or whatever that is in bra.?

steve_k
20-11-2008, 10:52 PM
http://www.youtube.com/watch?v=tUH-5vAYCx8&NR=1

thats in appreciation of your help

expat
21-11-2008, 08:04 PM
so for R410A it is about 550 psi or whatever that is in bra.?

I think it converts to about double D cup:D

steve_k
21-11-2008, 11:19 PM
I have come onto this forum and been completely honest in my skill level and lack of skills,
I expected quite a lot of flack, because it is easy to pick on the new plumber ac wannabe,

you have been very kind to me, given me information, you deserve credit and thanks for this,

this could of so easily been a slanging match telling me i have no business even looking at ac units,

as a direct result of the comments on this forum, I now have a nitrogen rig, proper scales and recovery unit on order,
I am getting my head around concepts i had not even hear of 1 week ago

Thx for your helpful posts, you may make a competent installer out of me yet

Steve

steve_k
22-11-2008, 07:44 PM
I think my head is going to pop I ave read that much in the last week,

I have some more questions,
Pressure testing, on a domestic 410a split, am i supposed to have the pipework disconnected from the outside unit? this would mean i am not testing the joints to the compressor (50% of the joints) obviously i would vacuum test it afterwards,

Superheat, yes I know stop trying to run before I can even walk,
anyhow, I have been trying to get my head around this, All the article's and posts say to take a temperature reading with your gauge connected to the suction line,
I have a dedicated 410a gauge, it obviously reads pressure and not temperature, If i got a reading of say 15bar or 220psi do I then use a PT chart to obtain the temperature, so for 15 bar I would have 58 Oc, if this is correct what are the R410a marking for on my gauge? they are at 0 at 100psi and then marked in +- around the gauge,

sorry if this is all a bit basic
Steve

dogma
22-11-2008, 11:32 PM
Hi steve, I like to pressurise after I connect the pipes to the outdoor unit. If I find a leak and it's in the service valves, leaking ofn back into the outdoor unit, I call the OEM and let them know their service valves are leaking.


Also I llike to cut the flare connectors off of the indoor unit and braise my pipes. Make sure you use 15% silver solder. 5 % is cheaper but should not be used with R410a pipe work. I find it's safer to cut and braise... I also take out the philips head screws from the electrical side and service valve cover and replace with safty screws which you can't undo with a normal screwdriver.


I know of installers that won't flare at all and braise all their pipes, even to the outdoor unit so the system is hermetically sealed and can't be tampered with...



_DOGMA-

just chilling
23-11-2008, 05:34 AM
writing on forums is new to me. so see how we go?

1. flux is not needed when brazing copper to copper if you are using correct rods.
2. if you are welding/brazing dis similar metals e.g brass to copper or brass to steel etc you will need flux or ready fluxed rods.
3. the only type of expander/swager for 1/4 ids manual flaring/swaging block type. imperial eastman make them you can get the at fridge wholesalers. but it is far easier to use a piece of 3/8 copper and sleeve it like a welded union/connector.
4. i live in australia now but worked as a fridgie in the UK. i expect you have to be licenced some how to handle refrigerant in spain. or most likely you will face heavy fines/imprisonment.
split air conditioners are critically charged with exactly the correct amount of refrigerant weight. useing digital scales and charging to the specified weight on the equipment label.
5.if you did not evacuate after the repair with a vacuum pump it is most likely the unit has moisture in it and will most likely suffer a burn out and render the whole system acidic.
6. a good book to buy and read is modern refrigeration and air conditioning written in america by Althouse Turnquist and Braccianno ISBN number
1-56637-300-x

just chilling
23-11-2008, 06:16 AM
i am so new i did not see more than a week of discussion.
another tip i have for you now i have read all the above.
if you look at your refrigerant gauges you will notice different colours of scale incremements around the crcumferance of the gauge the different coulours repesent different refrigerants and they will be wrote on the gauge for each colour e.g blue = R 134a and red may be = R407c etc. the pressure corresponds to the satuated temperature.
you will see R22 = 0 degC at 400KPA or 60 psig
also R407C = 0 degC at 400kpa or 60 psig. this will save you having to get a pressure temp table out all the time.

steve_k
23-11-2008, 05:24 PM
Hi
I have that book, just not had the 2 years it would take to read it, though i have been trying

I am going to find out about my legal responsibilities here in Spain, though I would not be capable of going on a Spanish course, maybe a UK ticket will cover me, also been thinking about the approved installers course Dakin etc, again this would have to be a trip back to the UK,


and a recovery unit is now on my shopping list

Brian_UK
23-11-2008, 11:26 PM
Thanks for your helpful posts, you may make a competent installer out of me yet

SteveSteady there Steve they'll be after commission next ;)

Also, on behalf of the others here, thanks for your kind words. :)

paul_h
24-11-2008, 01:10 PM
I have come onto this forum and been completely honest in my skill level and lack of skills,
I expected quite a lot of flack, because it is easy to pick on the new plumber ac wannabe,

you have been very kind to me, given me information, you deserve credit and thanks for this,

this could of so easily been a slanging match telling me i have no business even looking at ac units,

as a direct result of the comments on this forum, I now have a nitrogen rig, proper scales and recovery unit on order,
I am getting my head around concepts i had not even hear of 1 week ago

Thx for your helpful posts, you may make a competent installer out of me yet

Steve
Because you came here asking how to do the job properly, you didn't get any flack or were told to bugger off :D
If you were a plumber/electrician in australia who installed splits, I wouldn't give you the time of day. They are dodgy buggers who never do the job right, only care about doing the job as cheap and quick as possible and getting their money, never to return.
Then again, they wouldn't dream of doing/learning anything they are not paid to do, so unlikely to see any plumbers or electrician installers from here looking at RE.

When I saw your post I held off saying anything, as I didn't want to help those type of people due to the crap they threw in my lap when I did warranty for them. (They can't flare for ****, don't pressure test, don't evacuate, don't fit isolators).

But the fact you are here because you want to do the job right, to learn and you have a good attitude about it, is why you didn't get your marching orders :)

Also Nike123 started out as a electrican and installer I do believe. So some of you installers in europe can come good :D

steve_k
24-11-2008, 05:40 PM
Paul_H

reading through some older posts i came across a thread where you and other where voicing your dislike of plumber AC wannabes, baring that thread in mind your comments here are extremely welcome,

Back in the UK 100% of my work came from recommendations and repeat customers, and I have never advertised in 22 years of being self employed, I have only been working here in Spain for a year and I am finding it much different,

Attitudes are different, maybe they will catch up, and maybe they are different in the commercial sector, but on the domestic side attitudes are very lax
Today I have been to my suppliers to order a recovery unit, I have no idea how to use one yet:p
I asked about my legal responsibilities when fitting/handling refrigerants,
Yes I am supposed to have a handling ticket, I am supposed to have a recovery unit, and be registered financially with the government
we agreed that my attending a spanish course would be a waist of time because of my Spanish, a UK ticket is worthless, so do I have a problem?
he told me out of about 100 installers buying from him maybe 5 or 6 have a recovery unit and licence, and at most 30 are registered with the government (pay taxes)
when I asked about disposing of gas he looked at me as if I was stupid, as said that people wont pay for that lol.

OK telling you how bad everybody else is wont make me any more competent will it:) just trying to give you an understanding of how it is here.

I intend only to fit domestic split/multi split units, I now have (or is coming) all the tools i need to install and commission these units, If I ever have a problem I need to determine that it is not the electrical connection and that it is properly charged, anything outside of this would be down to the relevant service engineer (one of you)

Remember for you this type of install is basic grunt work

steve_k
24-11-2008, 08:16 PM
just a quick thought,

how many of you wouldn't think twice about installing a sink/bath/fused spur etc,

I would hope that the level of competence required to get to your skill levels, that the above would be very easy for you,
with a bit of reading/searching the net, how many would tackle a central heating installation? you already have 95% of the skills right?
maybe running a new circuit back to the fuse board and adding a new breaker?
maybe adding a new board because there is not enough space in the old board?

Brian_UK
24-11-2008, 10:23 PM
Steve, a set of recovery machine instructions if you want to add more to your reading list ;)

http://www.mastercool.com/media/69000-INST-ENG-BW_web.pdf

steve_k
25-11-2008, 08:18 AM
Thx brian
the unit i have ordered looks the same as the mastercool http://www.stag.es/detail.asp?Id=4002276

no doubt the instructions will be in Spanish

I have the chance of getting a new split air-con unit for 100e, Its one of those no name Chinese imports somebody purchased and no longer wants (still in box) I am thinking of getting this to practice on, the first time i use the unit shouldn't be on a customers unit lol,

quick question
If I use the recovery unit to recover 407 then recharge the 407 back to the AC unit leaving the bottle empty, can i then use the bottle to do the same for 410a? I am thinking about cross contamination from ant residual gas,

paul_h
25-11-2008, 09:00 AM
If you're going to reclaim for disposal, and cylinder will do.
If you are going to reclaim to reuse, you must use a new clean cylinder, new drier, fully purged out reclaimer.
Certified clean cylinders are available from wholesalers for rent.

Most of the time when you are reclaiming it's because the a/c has a problem, and the refrigerant could have been tainted, so not worth reusing it.
I've only reused refrigerant a few times, when an a/c was playing up and we thought it may be short. So we reclaimed it into a new reclaim cylinder and weighed it. If it was correct, it was charged back in. If it was short, the reclaimed refrigerant was disposed off anyway and a leak repaired and recharged with new refrigerant.
I don't like reusing refrigerant, even if it weighs right, it could have air or nitrogen in it. Also when 404a, r407c and r410a had a leak, the different gasses that make up the refrigerant leak in different quantiies, so you'll never have the unit working as good as it should after a leak repair if you reuse some of the original refrigerant.
edit: thats general advice for someone repairing splits where they often dont have more than 5kg refrigerant, so it's not worth the hassle dealing with the old refrigerant. It may be different for commercial when you have 20kg+

icecube51
25-11-2008, 06:18 PM
I don't like reusing refrigerant, even if it weighs right, it could have air or nitrogen in it. Also when 404a, r407c and r410a had a leak, the different gasses that make up the refrigerant leak in different quantiies, so you'll never have the unit working as good as it should after a leak repair
Yo Paul_h,
was of the same opinion, but Peter_1 proved me wrong. somewhere on this forum he left a script from Switzerland ho explanes it all.

Ice

steve_k
25-11-2008, 11:46 PM
Tonight i have borrowed some of Franks beer
beer makes you talk bollocks,

as a logical plumber you have the refrigerant working in the opposite direction, in fact if you asked most people to feel the high and low side of the outside unit they would get the flow and return wrong, 99& of plumbers would,
sorry frank you can have your beer back now,

Brian_UK
25-11-2008, 11:54 PM
Sleep well.....

technique
28-11-2008, 11:21 AM
Hi Steve,
We are a UK based AC and Refrigeration training company and have had a couple of people in Spain asking for training, we are looking at putting on a AC installation and safe handling course in the Torrevieja area early next year.. This we are going to 'tailor' to the Spanish market.. My experience of most ac engineers in Spain is that they have never heard of Nitrogen, vac pumps, benders and most scarily 'gauges'.. If you are intersted pm me and i'll let you know the details..

steve_k
04-12-2008, 11:29 AM
Today I had a good opportunity to learn, or so i thought

My friends split inverter unit stopped working, I had purchased the units from my supplier to get better discount for him, though i had not installed them, one of the units stopped working in heating mode, so still under guarantee the service engineer was called out,
after the first visit he decided the inverter was faulty, though he couldn't find out what the error codes meant (p9/e9 on a verhal split) he determined this by attaching his gauge and clamp meter, watching the pressure and load,

visit 2 was with the reign inverter, much cussing and a revisit scheduled for today,

today he turns up with a new external unit, takes the entire circuit boards out and swaps them with the installed unit, and guess what? no difference,

after a phone call to his boss he tells me he is going to replace the entire unit,

purging down? this was done by closing the valves and loosening the pipe work, venting the gas into the air,
torque wrench? obviously no idea what one of these where
vacuum pump, yes he had a vacuum pump, I think he had salvaged it from the arc, no servo valve, and he stopped it before cracking open the service valve,(not being closed on the manifold to hold the vacuum)
no pressure or vacuum testing,
leak tested with soapy water,

sort of puts things into perspective for me

icecube51
04-12-2008, 06:30 PM
if you try to tell these people how to do it the wright way,they just laugh at you and tell you he had it from his grandfather,ho did it for over 25years like that,so there is nothing wrong whit his way of service,its just the engines ho are no more like they joust to be.;)

Ice

icecube51
04-12-2008, 06:36 PM
Yo Steve,
i was in Spain this summer the hole mond of august, and call it a professions habit to look at other people 's work. so some new buildings whit AC's and to tell you the truth,if they do a job like that at my place,i just shoot the guy whit a magnum.

there is still a lot of teaching to do over there.;)

Ice

steve_k
04-12-2008, 09:48 PM
Ice I agree

If you read this thread from the beginning you will see I am not an hvac professional, but i am trying to do my limited work correct,
today made me realise what level of engineer operates in my area

jcook1982
25-01-2010, 03:52 PM
Grew up with psi.....a bar is where I go for a drink! :D

With regard to Copper sizes.....most copper used is still in imperial sizes 1/4, (5/16), 3/8, 1/2, 5/8. These are the sizes that you will come across for a/c.
You might find that metric sizes are used in spain, but the flare nuts on the a/c units are normally sized for imperial (at least in UK), so this could present you with a problem area? (i.e. leaks) (poor flare joints are one of the major areas for leaks).

Can you get pre-insulated coils of soft copper over in spain - often co-joined pairs of the two sizes i.e. 1/4 and 3/8.
You do not then need to braze, as you run a continuous length of pipe, and just flare join at each end.
Its worth investing in a decent eccentric flaring tool suitable for R410 joints. You should also invest in flare nut torque tools so joints are not overtightened.


I think that people should just cut the flares out and braze in whatever they need to connect. Brazing is not difficult. Flares seem to me if you tighten them too much or not enough you have a leak. (BOOOOOOO):o