Hi everyone
one of my client's ice maker evap and cond and comp
full of water because of hole...
ı cleaned up system with N2 etc.
can you help me what can ı do
ı dont want to change evap and condenser
ı will change the comp of course
thank you :D
The MG Pony
15-11-2008, 07:40 PM
Flush the system with Rx-11 or Methyle alcohol then pull a deep 500 or better micron vacuum. Drain the oil out of the compressor and flush it well, heat it up to 60c and pull a deep vac, add new oil and braze the system up. Pull a deep vacuum while heating the system untill it is to 500microns or better.
Recharge and test SH and SC
nevzat
16-11-2008, 02:31 AM
Thank you very much
wambat
16-11-2008, 04:59 AM
Flush the system with Rx-11 or Methyle alcohol then pull a deep 500 or better micron vacuum. Drain the oil out of the compressor and flush it well, heat it up to 60c and pull a deep vac, add new oil and braze the system up. Pull a deep vacuum while heating the system untill it is to 500microns or better.
Recharge and test SH and SC
If it has POE oil, a vacuum will not remove all of the moisture you need to install a liquid line drier also
The MG Pony
16-11-2008, 05:33 PM
One would hope that would be compulsery!