IARP ECX600 Upright chiller which according to the customer has been loosing gas every couple of months. He has been spending a fortune on people coming over to 'top it up' for the last three years!!!

I pressure tested and found the Evaporator has four very small pin hole leaks. The evaporator is badly corroded and needs replacing. Has anyone replaced one? Looks pretty awkward!

Not sure who supplies IARP spares either so any help on that would be appreciated.

Unit possibly 10 years+ old

Many Thanks

Lucas.

Mark
03-03-2004, 09:01 AM
Hi lucas:)

Yes familiar with the cabinet,where on the evaparator are the leaks can they be repaired ?.I have repaired leaks in the past on the knuckles and pipework.If not spares available from:

GH england
chipenham,
wiltshire,
(01249)449300


Regards Mark:)

chemi-cool
03-03-2004, 02:37 PM
hi lucas,

you can also get information at http://www.iarp.it/Cater-prod_ECX_600.html#

whec such problems start, it is best to install a new evaporator and if the original is of bad qulity, you can have a new one made by any coil manufacturer and it should be cheeper.


chemi :)

Peter_1
03-03-2004, 03:33 PM
Is this a tube in tube or a plate evaporator or are we perhaps talking abouth the condensor?

Lucas
12-03-2004, 12:34 PM
Thanks for all info.

Three of the leaks are repairable but the forth isn't due to its position.

The Evap is badly corroded so even if repair was possible who knows how long it would be before more leaks appeared.