23-10-2008, 11:13 AM
We have industrial chillers and the PRV just vent into the plant room and there is no additional extract from the plant room, I cannot find anything concerning venting of the plant room is there something in ASHRAE or is there a legal design requirement for the ventilation in the event of an accidental discharge
taz24
23-10-2008, 11:34 AM
We have industrial chillers and the PRV just vent into the plant room and there is no additional extract from the plant room, I cannot find anything concerning venting of the plant room is there something in ASHRAE or is there a legal design requirement for the ventilation in the event of an accidental discharge
You need a European document called
BS EN 378 its in four sections you need section two.
http://products.ihs.com/BS-SEO/30017319.htm
See also
http://products.ihs.com/BS-SEO/gbm16_17.htm
It is the specification the will give you all the information you need.
From memory all venting must be done to an external point.
Cheers taz.