View Full Version : Pressure Releif Valves


NickS
23-10-2008, 11:13 AM
We have industrial chillers and the PRV just vent into the plant room and there is no additional extract from the plant room, I cannot find anything concerning venting of the plant room is there something in ASHRAE or is there a legal design requirement for the ventilation in the event of an accidental discharge

taz24
23-10-2008, 11:34 AM
We have industrial chillers and the PRV just vent into the plant room and there is no additional extract from the plant room, I cannot find anything concerning venting of the plant room is there something in ASHRAE or is there a legal design requirement for the ventilation in the event of an accidental discharge


You need a European document called

BS EN 378 its in four sections you need section two.

http://products.ihs.com/BS-SEO/30017319.htm


See also

http://products.ihs.com/BS-SEO/gbm16_17.htm

It is the specification the will give you all the information you need.

From memory all venting must be done to an external point.

Cheers taz.