View Full Version : Which chilling system?



chemi-cool
14-10-2008, 09:05 PM
I am involved with building of new hatchery,

They will need about 100 TR water chiller for cooling the hatching cells and Ac.

I am thinking of manufacture the chiller myself.

There are a few cooling methods:

Falling film chiller
Shel & tube
Plate heat exchanger
Ice builder

what would you prefer and why?

US Iceman
14-10-2008, 10:40 PM
Plate & frame (or brazed plates) to limit refrigerant charge.

An ice builder if you have On-Peak & Off-Peak electrical rates.

abet_meneses
17-10-2008, 02:30 PM
prefer plate heat exchanger if water average temp is 33 to 36 fahrenheit.we have done this before on poultry proccessing.

regards

michaelm
17-10-2008, 07:42 PM
B"H
Hello Chemi,
No enough information:
type of water (sea or fresh?)
tem-re range
if the cleaning of the surface is needed

michaelm
17-10-2008, 07:50 PM
B"H
I would agree with US Iceman

baskaran
26-11-2008, 08:18 PM
water chilling for chicken cutting section they used,the water temperature req is 5 deg , this one is closed system during night time the chiller got freezed, the running pressure is 4.5bar, what temp and pressure the chiller got freezed?