View Full Version : Copper pipes pressure test



2007eng
12-10-2008, 01:42 PM
Hi guys.

I'm going to start a pressure test for 30 hp VRV-WII piping sysem.
DAIKIN said don't pressurize more than 40.
Our ambient temperature is variable and we afraid from the increasing of the pressure (causing damages in the equipments) due to temp increasing.
Can I decrease the test pressure to 35 bar to prevent the damages. Is 35 enough?
Thanks.

nike123
12-10-2008, 04:47 PM
You should do piping test before connecting equipment!

Rise in pressure is 0,1bar per 1K ambient temperature rise! Predict highest temperature and pressurize according to difference in expected and present temperature.

2007eng
13-10-2008, 12:05 PM
You should do piping test before connecting equipment!

Rise in pressure is 0,1bar per 1K ambient temperature rise! Predict highest temperature and pressurize according to difference in expected and present temperature.

Ok nike, very nice information.
By the way I will do piping test after connecting equipment to test the flare connections (in& out).

Thanks nike I will carrying out my test at 39 bars according to your informations.

nike123
13-10-2008, 12:37 PM
Ok nike, very nice information.
By the way I will do piping test after connecting equipment to test the flare connections (in& out).

That is leak test!
It doesn't need to be carried out at that high pressure, and also you have possibility that nitrogen goes to outdoor unit thru leaking valves and you end up with non-condensables in system.
For leak test with nitrogen 15 bar/12-24 hours is sufficient. Note ambient temperatures and pressures after temperature is equalized after pressurization (~2 hours later) and at the end of test.

2007eng
13-10-2008, 12:47 PM
Hi nike,
The normal operation compresser pressur is 38 bar, you know that if there is a minor leaks on the system its dosn't appear when testing under low pressur.

nike123
13-10-2008, 01:15 PM
Hi nike,
The normal operation compresser pressur is 38 bar, you know that if there is a minor leaks on the system its dosn't appear when testing under low pressur.


I am sure that leaks at flares will show up even at 15 bar!
But, you stick with what is manufacturer said!
I usually make all piping work before and do pressure test at 45 bar. and then connect equipment and test with nitrogen and trace gas (r22) at 15 bar with electronic leak detector. No leaks yet!

2007eng
13-10-2008, 01:27 PM
I usually make all piping work before and do pressure test at 45 bar. and then connect equipment and test with nitrogen and trace gas (r22) at 15 bar with electronic leak detector. No leaks yet!

By these steps I agree.
I'm very happy to exchanging experience with a man like you.

Thanks nike.

nike123
13-10-2008, 01:47 PM
By these steps I agree.
I'm very happy to exchanging experience with a man like you.

Thanks nike.

I am glad to help!

NoNickName
13-10-2008, 02:11 PM
Is that a pressure burst test or a leak test?
Leak test can be done at any pressure, while the pressure test has to be done in accordance with your country safety codes. Here in the EU it is according to 97/23/EC directive (PED)

2007eng
13-10-2008, 02:39 PM
Is that a pressure burst test or a leak test?
Leak test can be done at any pressure, while the pressure test has to be done in accordance with your country safety codes. Here in the EU it is according to 97/23/EC directive (PED)

It's a leak test. Thank you for this point

Chill'D
13-10-2008, 09:11 PM
Hi,

From what I remember its.....

leak test 1.1 x mwp
strength test 1.3 x mwp
(maximum working pressure)

But if daikin tell you to not go over 40 bar you shouldn't.

Cheers.

2007eng
14-10-2008, 08:56 AM
Hi,

From what I remember its.....

leak test 1.1 x mwp
strength test 1.3 x mwp
(maximum working pressure)

But if daikin tell you to not go over 40 bar you shouldn't.

Cheers.

Thanks for help.