View Full Version : Carrier 50YQ048



johno12345
18-09-2008, 09:28 AM
Hi,

We have a carrier 50YQ heat pump with a faulty stat, currently cooling the room to 50f blowing air at 40f! its a little chilly.

The wiring on the system are only labeled as R, W2, O, Y, G, E, C Can you still get stats for such a system and are the terminal identifications a standard?

Thanks :)

Grizzly
18-09-2008, 05:48 PM
Hi,

We have a carrier 50YQ heat pump with a faulty stat, currently cooling the room to 50f blowing air at 40f! its a little chilly.

The wiring on the system are only labeled as R, W2, O, Y, G, E, C Can you still get stats for such a system and are the terminal identifications a standard?

Thanks :)
Johno
I have trawled the Carrier website and have downloaded the manuel for this unit.
Which is listed as Obsolete, below is attached three pages with the wiring and thermostat details.
More importantly it gives the Carrier Part No for the stat.
Carrier may be able to help or advise??
Grizzly

Brian_UK
18-09-2008, 11:45 PM
Yes, those terminal references are still used by Carrier and also Honeywell I believe.