View Full Version : Choke test for new piping



multisync
29-08-2008, 09:56 AM
We have been asked to quote a VRV III and 'do' a choke test on the pipes. Now in all honesty I don't think we have ever done one or been asked. Has anyone else been and if so is it just a blast with nitrogen or is it more detailed.

Multisync
London

Argus
29-08-2008, 11:58 AM
.

Choke test?

Never heard that term used in that connection.
Why not play daft and ask what they mean by a choke test.


.

Brian_UK
29-08-2008, 11:13 PM
A choke test seems to refer to blocked capillaries where they have been brazed into other components.

The test would involve blowing nitrogen through the particular section.

Whether they mean the larger pipe sizes or not ......

Example here, top right of page under 'Practices'.

http://www.itpi.co.in/Resources/Ozone_depletion/Good%20refrigeration%20servicing%20practices%201106.pdf

But to be safe I would suggest doing as Argus suggests and asking the question of them as the task could be a bit open ended (sic).