mcunliffe4
07-08-2008, 09:37 PM
I went to site to look at hubburd premium cellar cooler high temp, on arrival found copeland scroll comp out on internal overload. Cooled comp down and blew cond coil with ofn as very dirty. Con had been relocated about a month ago, now the unit is at high level about 20ft but no p trap in pipe work as it goes up some trunking. Could anyone tell me why the compressor is doing this, is it because not enough oil returning in suction line?. Any suggestions would be very welcome.

nike123
07-08-2008, 10:07 PM
I went to site to look at hubburd premium cellar cooler high temp, on arrival found copeland scroll comp out on internal overload. Cooled comp down and blew cond coil with ofn as very dirty. Con had been relocated about a month ago, now the unit is at high level about 20ft but no p trap in pipe work as it goes up some trunking. Could anyone tell me why the compressor is doing this, is it because not enough oil returning in suction line?. Any suggestions would be very welcome.


Maybe now, when you cleaned condenser, thermal overload will stop acting.
Why don't you make full audit of system to know what is really happening in there?