PDA

View Full Version : Tempering



JIM ROBERTS
30-07-2008, 11:32 AM
Hi all,
I'm looking at a project to de-frost frozen products up to ambient in as short a time as possible.
This will be done in a room measring 13 x 6 metres, I'm considering using an evap with electric heating elements wit the fans operating at the same time, does anyone know any other method?

Tesla
30-07-2008, 12:13 PM
Microwave oven, Pressure defroster, Blast defroster, other than that your on the right track but I'm not sure about the evap unless your product is releasing moisture?

JIM ROBERTS
30-07-2008, 12:26 PM
The product will be releasing moisture which will be controlled by a de- humdifier

technomad
30-07-2008, 12:52 PM
Well if you have a defrosting room you must also so have a cold store or similar. How about reclaiming the energy from this room with a second condenser? And sell it as environmentally friendly.

chemi-cool
30-07-2008, 04:01 PM
Heat pump in heating mode will give you the cheapest hot air.
Don't you have a maximum temp?