View Full Version : panasonic fault code f31 needed.



coolflow
27-07-2008, 01:09 PM
Hi to you all hope that every one is enjoying there sundy off work but theres no rest for the wkd or the scint!. But dose any one have a list of fault codes for a panasonic ducted inverter system i have the code of f31 about 5mins after the comp and fans start on cooling mode.I dident try heat as its allready 34c in the appartment .any help please???:confused:

sinewave
27-07-2008, 06:20 PM
Have a decko here!

http://www.panasonic.com/consumer_electronics/bp_split_ac/manuals.asp

coolflow
27-07-2008, 08:47 PM
hi looked at that early to no avale.all seams like splits. and this is ducted inverter 2006 model. I am sure some one has the fault PLEASE!!

coolflow
28-07-2008, 07:51 PM
come on some one must know!!!!

superswill
28-07-2008, 08:36 PM
come on some one must know!!!!


on the list i have its low pressure,sounds like a decant,pressure test is in order

Chunk
28-07-2008, 10:45 PM
Type this website in www.aircon.ru.pbc_download/files/f1210657251.pdf (http://www.aircon.ru.pbc_download/files/f1210657251.pdf)

or if that dont work type "panasonic fault codes" into google and the above thing is number 5 on page 5.

Everything about panasonics.The webpage comes up as Front Cover 2006/2007 on google.

stefs_cruiser
18-08-2008, 04:30 AM
There are a couple of F31 faults
F31-01 Low suction pressure
F31-02 High pressure
F31-06 4 way valve not working
F31-10 valves shut or no refrigerant