Please can any one tell me the best way to re-adjust the expansion valve for chiller have three reciprocating compressors working in parallel
Best regard.

GXMPLX
17-07-2008, 01:36 AM
Read these first:

http://www.refrigeration-engineer.com/forums/showthread.php?t=11903

http://www.refrigeration-engineer.com/forums/showthread.php?t=13119

If you don’t have a correctly sized suction accumulator or your collector cannot hold enough liquid, think it over!

If your system has several expansion valves in parallel you have to study first if they affect each other. If they do it is better to adjust one at a time with the others closed.

Check the valve manufacturer website for information on how to adjust it!

Noori
17-07-2008, 01:14 PM
Dear Sir.
The chiller has one Danfoss expansion valve and I follow the necessary information for this type of expansion valve but I still have the ice collection in the suction line and the three compressors with suction pressure near the 40 psi. the system use R22.
best regard.

The Viking
17-07-2008, 06:49 PM
Dear Sir.
The chiller has one Danfoss expansion valve and I follow the necessary information for this type of expansion valve but I still have the ice collection in the suction line and the three compressors with suction pressure near the 40 psi. the system use R22.
best regard.


1. Ensure that you got enough refrigerant in the circuit. (measure subcooling/look in sightglass)

2. Ensure that enough water/fluid is passing through the heat exchanger.

3. Ensure that any and all driers/strainers are without blockage.

4. Measure the superheat and take actions as necessary.

PRESSURES ALONE DOESN'T TELL US/YOU ANYTHING.