just wondering if anyone else has had a high failure on sainsburys sites with the ir33 case controllers, as one site thats about three years old has a large failure rate with controllers just burning out and switching off.:D
bernard
16-07-2008, 01:51 PM
Hi
Yes I,ve had a few problems with burning out.Also found them double defrosting due to them loosing their time.I think carel are replacing all controllers from a certain batch.
Regards B
Chunk
16-07-2008, 09:07 PM
I know it sounds odd but,i havent had one failure yet of the ir33 apart from the double defrost(etc alarm).Yet i have had probably 30 or so rdm controllers blowing up on me.
coolhibby1875
17-07-2008, 07:02 PM
its amazing in the last 5 years i have only ever changed 1 rdm controller and it never even needed changing (condemend by a.n.other)however since january i have changed 6 carel ir33 controllers in just 1 sainsburys store in edinburgh
Chunk
17-07-2008, 07:52 PM
its amazing in the last 5 years i have only ever changed 1 rdm controller and it never even needed changing (condemend by a.n.other)however since january i have changed 6 carel ir33 controllers in just 1 sainsburys store in edinburgh
Looks like Carel dont like the Scots:)
Porkington
21-07-2008, 09:57 PM
I've changed more RDM than Carel recently. However, last week was probe week.... 33 is the record!
careluk
01-08-2008, 10:48 AM
Please I would appreciate to know in which store you had such failures.
For burning out you mean the display is completely blank?
As regards the double defrost, while you set the scheduled defrost (td1, td2...) please set the minutes different than 00 mins.
Carel UK
After Sales Support
careluk
01-08-2008, 11:08 AM
its amazing in the last 5 years i have only ever changed 1 rdm controller and it never even needed changing (condemend by a.n.other)however since january i have changed 6 carel ir33 controllers in just 1 sainsburys store in edinburgh
Please can you advise the type of fault on our control?
Thanks
CArel UK
After sales support
Chunk
01-08-2008, 07:14 PM
As regards the double defrost, while you set the scheduled defrost (td1, td2...) please set the minutes different than 00 mins.
Carel UK
After Sales Support
Hello
I dont get you on this.All the controllers are set up as per carel data sheets,but we are not always getting the same cases coming up with the "ETC" alarm as they vary across the store,
For example lets say cab. 51 gets this alarm and doesnt do it again for 4 months.
I have gone through the controller settings on numerous occasions and couldnt find anything jumping out at me,and it sounds like it happens to a lot of Carels and in varied locations around the UK.
Other than these silly alarms,i cant fault you on much else.(I will keep looking for something though;))
coolhibby1875
01-08-2008, 08:23 PM
hi carel uk i have had 4 go down with burnt out contacts causing the casing to melt into a big melted lump wish i had taken pics now.
another one the screen was all blank and another i have changed due to double defrosts which now i have discovered is just dodggy settings.these controllers were all less than 6 months old.
careluk
05-08-2008, 01:33 PM
The eTC may be due to a very strong spurios noises. However this alarm does not affect the running of the controllers. The defrost will be performed according to the dI parameter instead (interval between defrosts).
coolhibby1875
30-08-2008, 08:37 PM
hi careuk does carel offer any training courses in the uk we are now doing lots of tesco express stores with the carel touch screen front ends and networked controllers i or my workmates have not encountered these
Keef_Controls
31-08-2008, 04:14 PM
Carel UK - can you explain why there's such a high voltage present on the RS485 line ? enough to feel quite a bit of shock ? I've seen this in loads of stores - and even noticed it in a test room...I'm convinced it not just "noise" pickup, and i'd be concerned about safety reg's if is was you...