PDA

View Full Version : "gunk" on stem of regulator valve



Freezer Burn
15-07-2008, 02:56 PM
The stem for manual operation of a regulating valve seized and couldn't turn the valve. After pulling it apart, found the threads on the stem full of "gunk". Wiped it off, but what is it and were did it come from. How do I keep it from happening again? Have a strainer before the valve.

US Iceman
15-07-2008, 03:08 PM
You did not give us much information to consider.

When you post a question, you need to provide more details such as; where is the valve installed? (liquid, suction, discharge, hot gas, or an oil line?)

What refrigerant is being used?

What are the operating conditions where the valve is installed? (pressure, temperature, etc.)

See what I mean? The more information you can supply helps us to help you. Odds are, one or more of our members may have already seen something like this.

Freezer Burn
15-07-2008, 06:45 PM
Thanks, this may help.
R717 system, liquid line, 125 psi, 90 degree F

nh3wizard
15-07-2008, 06:49 PM
Could be anything, oil, never seize, threadlocker...

keepitcool
15-07-2008, 06:53 PM
Could be graphite packing also. What color was it?