View Full Version : carrier 7 flash code???
coolflow
09-07-2008, 07:31 PM
Hi to you all.Dose any one know the fault for a 7 led flash code on a carrier casset 40kx048.?? It works for 20 mins then gose to fault,all the pressures are ok on r22 and it cools nice untill it packs up the fxxxx thing!!!!.any help please :rolleyes:
Brian_UK
09-07-2008, 11:50 PM
Coolflow, the Carrier file on the cassette doesn't seem to show any fault finding.
The outdoor unit should be a 38GL model and there are a few manuals for those. I've listed one here which shows the LED faults on page 21.
http://eto.carrier.com/litterature/iom/IM_38GLM_ENG.pdf
If it's not the right model try looking here for it
http://www.uk.carrier.com/sitemap.htm
Good luck.
coolflow
10-07-2008, 10:27 PM
Thanks a lot found the fault to be condensate pump?. so i will look tommorow and see if it is. thanks again .Ian
vBulletin® v3.7.4, Copyright ©2000-2008, Jelsoft Enterprises Ltd.