PDA

View Full Version : conversion



tarcau mihai
06-07-2008, 08:57 PM
Hy guys.. can enybody help me how many watts is 22 RLA or LRA??i have to install a group compressor -condenser and i don't have any specification on label just this...thks

BigJon3475
07-07-2008, 10:38 PM
22 RLA's tells you this is 71% of the maximum allowable current before the IOL will open.

22 LRA would be the amount in amperage the motor pulls when in a locked position or starting position.

You should look into ohm's law there within lies your answer.

Peter_1
08-07-2008, 07:43 AM
LRA is the current with a Locked Rotor and has nothing to do with MRA (Max Run Amps) or FLA (Full load Amps)
If you measure LRA, the you only know that the compressor is stuck.