PDA

View Full Version : pressure of floating condensation


german
24-06-2008, 05:33 AM
Hi
Any people know, pressure of floating condensation in refrigeration system for supermarket..
Thank you
Bye

GXMPLX
24-06-2008, 08:14 PM
It'll float! Thus it's name. Range of values will depend on condenser type and cooling fluid's temperature and/or ambient conditions.

US Iceman
24-06-2008, 10:51 PM
The condensing temperature can only float down to a value that does not negatively affect the system operation. There is a lower limit that should not be exceeded. This limit is determined by the equipment and components used and how they work dynamically together.

GXMPLX
25-06-2008, 12:51 AM
The condensing temperature can only float down to a value that does not negatively affect the system operation. There is a lower limit that should not be exceeded. This limit is determined by the equipment and components used and how they work dynamically together.

That limit is decided at design time, knowin nothing about the system it is arbitrary and free. Besides it can be changed. Adjusting TXV's lovers would like this!