View Full Version : Compressor motor protector module
marc5180
09-06-2008, 05:09 PM
I ordered a motor protector module for a copeland scroll weeks ago from our local wholesalers for a Climate packaged chilled water unit. I gave them the model of the chiller and the compressor and what i thought was the model of the module but i got a call saying i must have missed one of the letters off, now i'm sure that i haven't and if i have could anyone help me out :D
As far as i'm concerned its a INT 69SC. but he says i missed a letter off
http://img183.imageshack.us/img183/9150/24042008349nj5.jpg
Chunk
09-06-2008, 06:02 PM
Heres a download for copeland scroll
http://www.ecopeland.com/literature/eCopeland/EN_C060206_AGL_ZPSingle_0.pdf
Page 7
Int 69sc/carel
It might help:)
Chunk
09-06-2008, 06:19 PM
Marc Try this site
http://www.cmpcorp.com/ListModelParts.aspx?crID=KRIWAN&brand=KRIWAN
Shows pictures of different modules and model types.
nike123
09-06-2008, 06:23 PM
I ordered a motor protector module for a copeland scroll weeks ago from our local wholesalers for a Climate packaged chilled water unit. I gave them the model of the chiller and the compressor and what i thought was the model of the module but i got a call saying i must have missed one of the letters off, now i'm sure that i haven't and if i have could anyone help me out :D
As far as i'm concerned its a INT 69SC. but he says i missed a letter off
http://img183.imageshack.us/img183/9150/24042008349nj5.jpg
This is because he is stupid merchant and he has to sell you what he has on shelf.
Your model is right, and he thinks that it should be INT 69SCY (which has additional function of phase monitoring). You could also fit this one but you should make connections to the compressor power supply terminals.
http://www.cmpcorp.com/Kriwan_Products.asp#product2
marc5180
09-06-2008, 07:18 PM
Thaks for the help guys, i was sure i was right. I'll ring them tomorrow and confirm with him.
thankyou both of you
jelecto
09-06-2008, 09:47 PM
i will try to help u , first my english is no so well, cause i'm spanish speaking.
i will send to u , what the copeland compressor nomenclature mean , and in this way maibewill note, witch parte is missing.
in 5min i will send u another message, let me copilate the information
best regards javier
shooter
10-06-2008, 12:27 PM
a simple kriwan is good for the job any other unit for PTC will work too.
protect
20-06-2008, 09:19 PM
The INT 69 SC is a special version from copeland Scroll compressor. If you want to replace it the best way is to order it via priem source.
There are no other alternatives in the market because this products are special developed for copeland customized.
monkey spanners
20-06-2008, 10:08 PM
The early ones fitted to copeland scrolls where just ordianry style INT69's with no phase protection, same style as in the copeland and later prestcold semi's. Newer scrolls use the INT69SCY with phase sensing.
Jon
marc5180
21-06-2008, 04:39 PM
The suppliers were adamant that there was another letter after the INT 69SC, i have argued with them and shown them the above picture to prove it but he isn't having it so we have ordered thw INT 69SCY which has phase monitoring.
How different will the wiring be from the other one because i will be sent to change it and i dont want to get it wrong.
monkey spanners
21-06-2008, 05:37 PM
I think its just got an extra three wires that go to the compressor terminals to check the phases are in the right place.
Jon
marc5180
21-06-2008, 09:47 PM
I think its just got an extra three wires that go to the compressor terminals to check the phases are in the right place.
Jon
That sounds easy enough, thanks Jon
Powered by vBulletin® Version 4.2.1 Copyright © 2024 vBulletin Solutions, Inc. All rights reserved.