View Full Version : Water Chiller Gas Pressure ??



rajpatel
12-05-2008, 11:49 AM
Hi, anyone can say what is the high pressure of chiller having water cooled condenser. cond water inlet 36 deg.c

powell
12-05-2008, 02:52 PM
Which refrigerant?

Brian_UK
12-05-2008, 09:50 PM
As an HVAC Engineer you should know that we need more information to arrive at a sensible answer.

rajpatel
13-05-2008, 09:38 AM
REFRIGERANT IS R-22, COND WATER INLET IS 36 dEG.C
PLEASE LET ME KNOW

nike123
13-05-2008, 03:35 PM
REFRIGERANT IS R-22, COND WATER INLET IS 36 dEG.C
PLEASE LET ME KNOW

Do you have water regulating valve?

powell
13-05-2008, 04:46 PM
rajpatel

36 C = 97 F water inlet (for my benefit).

A typical water-cooled unit is designed for 75 to 80 F EWT. Using R-22 that would relate to about a 210 PSI head pressure. With 97 F EWT you might see about 255 PSI.

Of course this is just speculation without knowing GPH, type of condenser, pressure drop and the type of controlling the system has to regulate head pressure.

Brian_UK
14-05-2008, 12:41 AM
Also the leaving water temperature might be closer to the mark.