07-05-2008, 10:17 PM
Has anybody got list of climaveneta fault codes for HRAT (E06,E22) cant seem to find on the net, thanks
1torr
07-05-2008, 10:54 PM
Hello Kevin(us Kev's should stick together), if its a cvm 2, E06 is ST2 probe malfunction (connections 3&4 on board. E22 is circuit 2 low pressure, sounds like probe at evap outlet water temp isn't working and the comp is continuing to run on down and tripping LP.Hope this helps, let us know how it goes. Kev.
Grizzly
08-05-2008, 12:14 AM
Hello Kevin(us Kev's should stick together), if its a cvm 2, E06 is ST2 probe malfunction (connections 3&4 on board. E22 is circuit 2 low pressure, sounds like probe at evap outlet water temp isn't working and the comp is continuing to run on down and tripping LP.Hope this helps, let us know how it goes. Kev.
Hi Kevin.
Good to see you back!
How's tricks.
PM me if you wish?
Grizzly
KevinRPS
08-05-2008, 01:13 AM
Thanks 1torr that sounds right, back on site tomorrow will check it out
conor1967
05-07-2010, 04:47 PM
hi, working on a climavenete chiller today.its a be/srat and fault code e103 is coming up. this anyone know how to clear thism thanks
bill234
06-07-2010, 02:11 PM
air conditioning is the better solution in all aspects of air condition maintenance and repair
Grizzly
06-07-2010, 04:37 PM
air conditioning is the better solution in all aspects of air condition maintenance and repair
CHEAP SHOT Bill!
Seeing as the company you recommend forms the basis of your email address.
I can only assume that these last 2 posts are a attempt at Self promotion?
Please restrict your enthusiasm to Helping others as the rest of us do! :mad:
Grizzly
Spare Parts Man
22-07-2010, 07:04 PM
...E103 code indicates the compressor thermal overload protection, possible cause being the compressor motor overheating...