hi.

have a problen with a daikin vrv k series system from time to time, i have a u9 being displayed on a central controller with all associated indoors flashing same and a ue on the time schedule,it resets then after a while .. pointers anyone?

rgrds phil

superswill
23-04-2008, 07:27 PM
hi.

have a problen with a daikin vrv k series system from time to time, i have a u9 being displayed on a central controller with all associated indoors flashing same and a ue on the time schedule,it resets then after a while .. pointers anyone?

rgrds phil


U9:

system malfunction of tranmission between indoor and outdoor

systems being switched off at local spur's?
poor conections of comms wire?

are a few of the top of my head

frank
23-04-2008, 08:23 PM
Spot on Super

U9 normally occurs when the outdoor loses comms with one or more of the indoor units.

Most probable causes are:

1 - Indoor isolator switched off to one of the fan coils
2 - Comms wiring taken through the high float limit switch on the cond. pump

As it's flashing all of the indoors on the central controller, you should look at the indoor ring main power supply and also the 2 core interconnect wiring between the outdoor and the first fan coil.

The UE fault code indicates a break in the comms between the central controller and the indoor unit.

Try to trace the wiring or install a temporary 2 core to eliminate the problem