Hi.
I have moved a whole bunch of Daikin condenser units this week, from a mezzanine floor (now a production area) to the outside of the building.
One of the units was a Daikin R200 roof unit.
The system was working when removed. All refrigerant was removed from the system, the spinacle valves were closed down and the system de-piped and re-sited outside.
I have extended the pipework from the old location, through the external wall of the building and down to its new location in the car park.
The factory charge of the unit is 5.55 Kg (according to plate on condensor and Daikin tech support).
Charge is good for 7.5M of pipe, with an additional 50g/m thereafter.
Pipe run is 47M (with a max of 50) which gives a factory charge of 5.55 Kg and a trim charge thereabouts of 1.975 Kg.
Was hoping to trim the charge by Subcooling or Superheating method for optimum performace.
Unit was charged with OFN on Thu morning, left in the system for 24 Hours and dumped this morning after prooving the pipe work I have installed.
I vacuumed the system down until I hit about 900 microns, then left it while I had dinner and picked up some gas for another unit. I also had installed a site window to the liquid line (with wet dry indicator) which now shows as dry.
Also, I installed a 1 1/8" dryer into the gas suction line inside the unit before the copper feeds back to the spinacle valves.
Valves are open etc.
When the unit fires up, the compressor and two cooling fans start, then turn off abour 2 seconds later.
The legendary E0 code is appearing on the remote controls.
When I de-gassed the unit, it only had 3.5Kg of gas on board which makes me think it may be the High Pressure Switch playing up.
I suspect that it could be low pressure / high pressure / compressor overload and also read on this forum that there is a condensor fan monitoring circuit???
Does any one have experience with this problem, or can someone explain to me the best way to diagnose the problem?
Any advice would be greatly appreciated.
Flamer_The_Sparky
I have moved a whole bunch of Daikin condenser units this week, from a mezzanine floor (now a production area) to the outside of the building.
One of the units was a Daikin R200 roof unit.
The system was working when removed. All refrigerant was removed from the system, the spinacle valves were closed down and the system de-piped and re-sited outside.
I have extended the pipework from the old location, through the external wall of the building and down to its new location in the car park.
The factory charge of the unit is 5.55 Kg (according to plate on condensor and Daikin tech support).
Charge is good for 7.5M of pipe, with an additional 50g/m thereafter.
Pipe run is 47M (with a max of 50) which gives a factory charge of 5.55 Kg and a trim charge thereabouts of 1.975 Kg.
Was hoping to trim the charge by Subcooling or Superheating method for optimum performace.
Unit was charged with OFN on Thu morning, left in the system for 24 Hours and dumped this morning after prooving the pipe work I have installed.
I vacuumed the system down until I hit about 900 microns, then left it while I had dinner and picked up some gas for another unit. I also had installed a site window to the liquid line (with wet dry indicator) which now shows as dry.
Also, I installed a 1 1/8" dryer into the gas suction line inside the unit before the copper feeds back to the spinacle valves.
Valves are open etc.
When the unit fires up, the compressor and two cooling fans start, then turn off abour 2 seconds later.
The legendary E0 code is appearing on the remote controls.
When I de-gassed the unit, it only had 3.5Kg of gas on board which makes me think it may be the High Pressure Switch playing up.
I suspect that it could be low pressure / high pressure / compressor overload and also read on this forum that there is a condensor fan monitoring circuit???
Does any one have experience with this problem, or can someone explain to me the best way to diagnose the problem?
Any advice would be greatly appreciated.
Flamer_The_Sparky