View Full Version : How to find NH3 hermetic pump



sakchai21
11-04-2008, 05:28 AM
Which parameter have been considered? or only I just focus to total plant capacity.
How can we select the NH3 hermetic pump in the correct way. Or anyone has any link to explain for this?Thanks in advance.

US Iceman
11-04-2008, 03:02 PM
Here is a link to some basic information...

http://www.cornellpump.com/industrial/refliterature.htm

sodielectric
29-04-2008, 04:51 PM
A pump manufacturer will need the capacity (GPM), differential pressure (PSI), and temperature to make a pump selection for you.

Make sure the pump has an NPSHr around 1.5 to 2 ft less than NPSHa.

kelvin_27_84
07-05-2008, 05:15 PM
First to size a NH3 pump you need the flow speed (m/s), next you will need the meter head (m) this is how to calculate.

eg. if I have got 20 m vertical pipe from the pump, 100m horizontal after that. You will have to do this. (100 X 0.15) + 20m = 35m(head). The reason for using 100 X 0.15 is considering the friction loss on the pipe when it is running horizontally. For vertical you will need to use the full quantity. For the above, please consider the last evaporator the pump has got to pump.

Flow speed, normally from a pump vessel outlet we size the outlet to about (0.5m/s) on the outlet before the pump. But after that you will need to consider the flow neeeded to reach the last evaporator.

Lastly, a NH3 pump system is when u size 4:! circulation. This is the best.

kelvin_27_84
07-05-2008, 05:16 PM
Tell you what, PM me your e-mail I send you a sizing chart from Hermetic-pumpen to size your NH3 pump

ntfreezer
28-05-2008, 03:20 PM
hi,
tell me some details,I can help to select the correct ammonia pump.
http://www.worldbase.cn/introduce1.html

JERRYCOOL
31-07-2008, 06:05 AM
Flow rate adn the head,available power supply.That's all you need.

luissandoval
23-10-2008, 08:57 PM
"First to size a NH3 pump you need the flow speed (m/s), next you will need the meter head (m) this is how to calculate.

eg. if I have got 20 m vertical pipe from the pump, 100m horizontal after that. You will have to do this. (100 X 0.15) + 20m = 35m(head). The reason for using 100 X 0.15 is considering the friction loss on the pipe when it is running horizontally. For vertical you will need to use the full quantity. For the above, please consider the last evaporator the pump has got to pump."


what about pressure drop for fittings and valves.