PDA

View Full Version : heat exchanger


david2008
29-03-2008, 07:55 AM
Hello,
Both condenser and evaporator are heat exchanger. What type of heat exchanger are used in condenser, and what type for evaporator? (how to select heat exchanger for them?)
Thanks in advance.

David

The MG Pony
29-03-2008, 03:29 PM
First you calculate the total load in the box, determin the temp and RH you want, this will determin your evap duty and size.

From there you work back wards the condenser will be the last thing sized.

david2008
29-03-2008, 07:36 PM
Thank you MG pony!

david2008
29-03-2008, 07:42 PM
How about the type of heat exchanger? like fin and tube, plate and tube....

Josip
29-03-2008, 08:01 PM
Hi, david2008 :)

Welcome to RE forums....


Hello,
Both condenser and evaporator are heat exchanger. What type of heat exchanger are used in condenser, and what type for evaporator? (how to select heat exchanger for them?)
Thanks in advance.

David

selection of HE depends on use... and price;)

then we have a media for cooling (for condensers) both air and water or only air/water (or maybe another liquid)....

the same is with evaporators ... cooling only air or some liquid....

.... they can be also PHE-Plate Heat Exchangers, S&T-Shell&Tube, TinT-Tube in Tube, Finned or with Plates on tubes...maybe some other type which I do not know;)

hope this help a little..

Best regards, Josip :)

david2008
30-03-2008, 06:59 AM
Great! Thanks Josip. your post is helpful.

David

The MG Pony
30-03-2008, 05:07 PM
Lets cut more to the chase and ask: What exactly are you trying to do? as the application determines what is used.