View Full Version : Warehouse frost heave protection
samiam
21-03-2008, 03:56 PM
I am considering the following options for a warehouse floor to prevent problems associated with frost heave: So far I have used:
a) Electric heater mat.
b) warm glycol pipes.
c) Natural and forced ventilation.
I have used the electric mat and glycol heater pipes before, but not the forced ventilation.
What are you experiences/comments on the forced and natural ventilation methods?
Thanks
Grizzly
21-03-2008, 09:46 PM
I am considering the following options for a warehouse floor to prevent problems associated with frost heave: So far I have used:
a) Electric heater mat.
b) warm glycol pipes.
c) Natural and forced ventilation.
I have used the electric mat and glycol heater pipes before, but not the forced ventilation.
What are you experiences/comments on the forced and natural ventilation methods?
Thanks
Samiam.
I have many years experience with Cold Stores and like you understand the benefits and pitfalls of both A and B.
If by Natural you mean floors built on dwarf walls.
With 6 inch Concrete slabs on Insulation slabs.
Thereby having a thermal gap under the floor.
Then I understand and this is by far the most common for Large areas.
But I am not sure what "forced ventilation" is can you explain?
Grizzly
smpsmp45
23-03-2008, 06:10 AM
We generally use Forced Ventilation by embedding the pipes below the Flooring.
If you are interested I can send you a sketch as to how we do it.
Electrical mats is expensive proposal though we use that only for Blast freezers for -40 deg C.
We have used elevated floor in few cases, but again that also is expensive.
Kh1971
23-03-2008, 10:40 AM
HI,
The ventlation should be done before doing the cold store it self, if you are interesed send me a mail and I well send you the drawing how you can make the ventaltion for the flooring *** note that it is very good way and Iam using it here.
Khalid
US Iceman
23-03-2008, 07:42 PM
The forced ventilation system is when a fan blows the air through the underfloor pipes. The static version of this is the natural convection pipes that are open to the outside air.
I think the method you use depends entirely on the location of the cold storage. In areas where the climate is moderate or cold you would want a positive (heat source) method to provide heating for the floors.
In warm to hot climates the natural convection pipes may provide a suitable alternative. In this climate the ground temperature would remain fairly warm year-round so the underfloor pipes with natural convection air currents should be sufficient.
samiam
29-03-2008, 06:33 AM
Hi Gents,
smpsmp45 - please add the scketch to this forum
Thanks for the feedback - US Iceman (thank for the expalantion - it is as per my thinking)
Thanks
vBulletin® v3.7.3, Copyright ©2000-2008, Jelsoft Enterprises Ltd.