View Full Version : please I need help



mwinjuma
18-03-2008, 07:05 PM
I HAVE STAND FREEZER ACTUALLY IT OPERATE WELL BUT WHEN IT OFF,IT LATE TO START ITSELF.IT MAY TAKE 24HOURS OR 48HOURS.THE FREEZER IT USE PTC-RELAY AND HAS COMPRESSOR OF DANFOSS OF 1/5h.p AND I HAVE ALREADY INSTALL A FAN FOR COOLING OF COMPRESSOR AND IT USE R600a.I TRY TO USE PROPER CAPACITOR WITH PROPER RELAY BUT IT DOESN'T WORK. WHEN I RETURN THE PTC RELAY IT WORKS BUT THE SAME AS BEFORE.SO I NEED THE HELP WHAT SHOULD I DO IN ORDER TO WORK AS I NEED. I MEAN WHEN I OFF AFTER 15-30MINUTES TO SWITCH ON TO WORK AS PROPERLLY.

nike123
18-03-2008, 07:24 PM
I HAVE STAND FREEZER ACTUALLY IT OPERATE WELL BUT WHEN IT OFF,IT LATE TO START ITSELF.IT MAY TAKE 24HOURS OR 48HOURS.THE FREEZER IT USE PTC-RELAY AND HAS COMPRESSOR OF DANFOSS OF 1/5h.p AND I HAVE ALREADY INSTALL A FAN FOR COOLING OF COMPRESSOR AND IT USE R600a.I TRY TO USE PROPER CAPACITOR WITH PROPER RELAY BUT IT DOESN'T WORK. WHEN I RETURN THE PTC RELAY IT WORKS BUT THE SAME AS BEFORE.SO I NEED THE HELP WHAT SHOULD I DO IN ORDER TO WORK AS I NEED. I MEAN WHEN I OFF AFTER 15-30MINUTES TO SWITCH ON TO WORK AS PROPERLLY.


:eek:Please, don't use all capital letters in your posts because that is consider as shouting.

You should do some electrical measurements. Do you have voltage from thermostat when this is happening or not? If not, you should change thermostat. If you have voltage from thermostat, and compressor still doesn't start, you should check if voltage is present at both main and start winding. If it is present, that mean that compressor is overheating, and if it is not present on both or one of them, then it is starting device who is making problems and you should change it.

Electrocoolman
18-03-2008, 08:39 PM
Can you let us know the model number of the compressor please.

Does your compressor use a capacitor....what value and voltage