View Full Version : Unit coolers using glycol



tjk2007
15-03-2008, 10:23 AM
Dear All,

I need some details to my design.

Plant : Vegetables.
Refrigerant Ammonia
Secondary Coolant:38% Prop. Glycol.

The temp.for the rooms are as follows.

Raw Goods Vegtables Mixed: 4ºC

Cleaning & Sorting 4ºC

Processing 15ºC

Cleaning of dirty crates 22ºC

Finished Goods 0ºC

The above said are customer requirements. We cannot change.

Basically I consider the Room temp 0ºC and take the glycol temp. as follows

Temp in to the unit coolers: -14ºC
Temp Out from the unit coolers:-7ºC

My Question is

Is it possible to attain the room temp 22ºC in the same temperature program.
If not what is the solution for that.
Hope I will get some details.



Regards,



TJK

Brian_UK
16-03-2008, 12:33 AM
My Question is
Is it possible to attain the room temp 22ºC in the same temperature program.
If not what is the solution for that.Can you include a condenser coil in the 22°C room to provide heating?

What is the ambient air temperature in your region? Can ambient air be used for heating?

Samarjit Sen
16-03-2008, 03:06 AM
Remember Relative Humidity is important. The same should be 80 to 85%.

tjk2007
23-03-2008, 07:49 AM
[/font]
[/list]Can you include a condenser coil in the 22°C room to provide heating?

What is the ambient air temperature in your region? Can ambient air be used for heating?



Ambient Temp:53 C

The Condenser Coil is placed outside of the cold room only.ambient air be cannot be used for heating.Because The ambieent temp & RH are varying suddenly

Our Area Is UAE

Rgds,

TJK