15-03-2008, 12:43 AM
Another one for the supermarket rack lovers:
I´m trying to adjust the operation of two SORIT-20 EPRs connected in parallel, that set the evaporator pressure in a rack circuit. According to the instructions I found in the rack log, I´m suppose to initially "reset" both of the EPRs by turning their adjustment screws all the way in, and then gradually turn them out, a little bit at a time, simultaneously. At first, both of the EPRs get similarly cold, but after a few hours, one gets colder and the other noticeable warmer. I´ve repeated the same procedure several times, with the same results.
Both inlet pilot screens are clean. The EPRS were recently overhauled: new pistons, sleeves, O rings, springs and gaskets. Solenoid coils were not replaced but seem to be working all right. Any other recommendations?
I´m trying to adjust the operation of two SORIT-20 EPRs connected in parallel, that set the evaporator pressure in a rack circuit. According to the instructions I found in the rack log, I´m suppose to initially "reset" both of the EPRs by turning their adjustment screws all the way in, and then gradually turn them out, a little bit at a time, simultaneously. At first, both of the EPRs get similarly cold, but after a few hours, one gets colder and the other noticeable warmer. I´ve repeated the same procedure several times, with the same results.
Both inlet pilot screens are clean. The EPRS were recently overhauled: new pistons, sleeves, O rings, springs and gaskets. Solenoid coils were not replaced but seem to be working all right. Any other recommendations?