View Full Version : R407C and R22



hassan
05-03-2008, 11:42 AM
What is detail different bitween R407C and R22 ?
can we changs two gas together?
any feedback highly welcom

Hodgo
05-03-2008, 12:58 PM
What is the application? compressor? chiller? A few more clues please.

Springbok
05-03-2008, 01:44 PM
I wouldn't mix them if thats what you ment.If you want more specific readings and details,refer to the P-T Chart on the refrigerants.I take it its an Air Conditioner you're working on?

Brian_UK
06-03-2008, 12:10 AM
Check out the manufacturers websites for technical details of most refrigerants, such as here...

http://www.refrigerants.dupont.com/Suva/en_US/products/*****22.html

fridgey
09-03-2008, 02:35 PM
G'day, R22 is HCFC azetrope, R-407C is HFC non-azetrope meaning it has a temperature glide as its a blend of gases and must be liquid charged. It also requires polyester oil. R-407C is one of the replacements for R22 in most new A/C equipment and chillers from 10kw to 200kw.

powell
09-03-2008, 04:15 PM
hassan,

If you are inquiring about converting from R-22 to R407C follow this link to Copelands AE bulletin. The first paragraph will help with your decision.;)

http://www.hvacrinfo.com/cope_ae_bulletins/95-14.PDF

ice_cool
11-11-2008, 09:25 AM
it doesn't work to mix the two together.