hai guys i get one problem in carrier container freezer
defrost thermostat closing failure or open failure.
i changed new thermostat,but still there is same alarm appear.
what is range of closing temperature and open temperature of thermostat. how i can check the thermostat is deffecteive or effective.

nike123
02-03-2008, 10:21 PM
Generally speaking, if you changed thermostat with new one of same characteristics and you did not make mistake when wiring it, then thermostat is not cause of error.
Also, bare in mind, that alarm is active if temperatures in controlled space is not within acceptable working conditions.

powell
02-03-2008, 11:55 PM
rkmoorthy

A common setting for these controls would be:

Fan Delay cutout at +45 F and a cut in at +25 F.

Defrost termination approx 55 F