PDA

View Full Version : inverter problem



bangoman
29-02-2008, 02:40 PM
bn workin on agean inverter its displayin E2 on indoor display panel and code means phase sequence error .Dnt understand wt they mean by that .The indoor shares an outdoor with the other which is operating ok

Springbok
29-02-2008, 03:28 PM
Need some info on the make and model of that unit,mate.Is the outdoor unit running?

bangoman
29-02-2008, 08:29 PM
The Make Is Agean And The Model Is As Below ;

Outdooor Unit Adv 80w

Indoor Unit One Adv V22g E

Indoor Unit Two Adv V71g E


The Other Unit Is Cooling Well & Outdoor Running Ok.

Brian_UK
01-03-2008, 08:54 PM
Check the wiring, contactors etc as it seems to think that may be the problem.

Springbok
01-03-2008, 10:31 PM
If the other unit is running,could be a wiring problem on the faulty one.Possibly somewhere on the pcb.probably a voltagedrop or something....

bangoman
05-03-2008, 01:41 PM
thnks guys seems was sum loose 2 core shielded comms cable .Hve rectified the fault.