28-02-2008, 10:04 AM
Hi all, ive been having trouble with a chiller unit going out on high pressure. The unit is on R404a and the high pressure is set to 350 psi, the unit did have an automatic reset high pressure switch but this was hammering everything when it was cutting out and coming back in. The unit is placed between the chiller and the wall of another building but the prevailing wind blows up the units date and can almost stop the wind flow. So we are considering moving the condenser on to top of chiller , but when i was there i decided to take a look at the sub cooling.. is it possible to have a higher sub cooling temp than the sct ?? does the unit have air or a mix of refrigerants in it?? or have i stuffed up taking the measurements. High was 235 psi or 36 deg C and the temp of pipe was 47 deg C, i was using a laser thermometer to test liquid line at reciever outlet.
cheers for any advice.

nike123
28-02-2008, 12:54 PM
When using laser (IC) thermometer you must adjust emissivity according to measuring surface if your instrument have that function, or you need to wrap 1 layer of black electrical isolating tape around pipe of witch you are measuring temperature.
You must be sure in your measured data before acting upon it.

US Iceman
28-02-2008, 05:45 PM
The unit is placed between the chiller and the wall of another building...


:eek:

Check the airflow on the air-cooled condenser to make sure it is not recirculating. An adjacent building wall and discharge air off of a condenser can do funny things to air flow.

Measure the temperatures of the air flow entering the condenser (all around the condenser inlet). If the air temperature measured is higher than the ambient dry bulb temperature away from the condenser you more than likely have air recirculation problems.

The warmer entering air reduces the condenser capacity and there is not much you can do to fix this than move the condenser to a location where it receives free air flow on all four sides.

Gary
28-02-2008, 05:49 PM
I keep a laser around for identifying hot spots (loose connections, burnt contacts, etc.) in electrical panels. Aside from that, I consider them unreliable and therefore pretty much useless.

Springbok
28-02-2008, 05:58 PM
Hey ChillTechnician...I would rather use a dial thermometer to be strpped onto the pipe,rather than a lazer,i find it more accurate readings are given.The temperature you have is pretty warm for the liquid line.Best to check the air flow in that surrounding area before thinking of air or moisture ( non condensables ) in the system.Is the sight glass fully charged?Good luck buddy...

Gary
28-02-2008, 06:17 PM
High was 235 psi or 36 deg C...

What was the ambient temp? And perhaps more relevant, what was the condenser entering air temp?

ChillTechnican
28-02-2008, 07:56 PM
Hey guys thanks for all replys, the system was fully charged but i was wondering if overcharged, ambient/air on was 22 C at time but no wind blowing.The feedback i get about laser is to only use it for pointing at a/c grilles to get an idea if they are working or similar indication . I will invest in a press on type today. Thanks all!!:)

Gary
28-02-2008, 08:33 PM
Hey guys thanks for all replys, the system was fully charged but i was wondering if overcharged, ambient/air on was 22 C at time but no wind blowing.The feedback i get about laser is to only use it for pointing at a/c grilles to get an idea if they are working or similar indication . I will invest in a press on type today. Thanks all!!:)

This gives you a TD of 36C - 22C = 14K/25F which is well within normal range. You can forget about noncondensables and probably overcharge, too.

The problem, as you have correctly identified, is almost certainly location in relation to the prevailing wind and the solution would be relocation and/or baffles to redirect the wind/prevent recirculation.

Dave Sewell
28-02-2008, 10:54 PM
Gary appears to have covered most avenues but somehow dicounts non-condensibles.
Disconnect the electrical supply to the compressor bot not the condenser fans.
Allow them to run idle for at least 30mins til all components are at ambient temperature then from the High side port measure the pressure and cros refrence to the saturated pressure relevant to ambient temp.
Well above would indicate air although your thermometer indicates an overcharge.
Also bear in mind refrigerant of this type should be charged in the liquid phase.
Have we a partial imbalance in the refrigerant composition?

DAVE

Gary
28-02-2008, 11:39 PM
Gary appears to have covered most avenues but somehow dicounts non-condensibles.


If the system had any appreciable amount of non-condensables, the TD would be much higher... but then it never hurts to check.

Gary
28-02-2008, 11:43 PM
Disconnect the electrical supply to the compressor bot not the condenser fans.
Allow them to run idle for at least 30mins til all components are at ambient temperature then from the High side port measure the pressure and cros refrence to the saturated pressure relevant to ambient temp.


Hmmm... you may want to close the king valve and pump down the system first.

SteinarN
29-02-2008, 12:38 AM
The correct way to determine any existence of non condensables is to measure the liquid subcooling at condenser outlet or receiver outlet. Assuming only minor hight differences and not any measurable pressure differences between condenser/receiver and not overfilled system there should be no measurable subcooling at condenser/receiver outlet. Any subcooling here is a certain symtom of non condensables in the system.

When there is sufficient refrigerant in the system, any non condensables will accumulate in the receiver bc only liquid is drawn out of the receiver and the non condensables (gasses) cant find the way to the bottom of the receiver where the outlet pipe is.

An example:
Lets say the liquid temperature (condenser outlet and receiver outlet) is 30 degres C, but you measure a condensing/receiver pressure of 15,1 bar. At 30 condensing/liquid outlet, the pressure should have been 13,1 bar! In this instance you have 2 bar additional pressure (15,1-13,1) in the receiver caused by non condensables. Lets say the gas phase volume of the receiver is 5 litres, then you have 10 litres of noncondensables at atmospheric pressure in the system. (10 litres at 1 atmosphere equals 5 litres at those 2 atmospheres additional pressure.) This is assuming that the temperature of the liquid surface in the receiver is the same temperature as the condenser outlet/receiver outlet. This assumtion should be valid in a system with short pipes between condenser and receiver, not any excess pressure loss between condenser outlet and receiver outlet and not considerably temperature difference between the condensing temperature and the surrounding air of the receiver.

When the system is stopped, the non condensables have a possibility to escape from the receiver and expand/dilute into a much larger volume of the system. That 10 litres of non condensables, when expanded/diluted in, lets say, 20 litres of the system, will cause an additional pressure above the saturated pressure of only 0,5 bar. (10 litres at 1 bar equals 20 litres at 0,5 bar) Thus it is far more accurate to measure the receiver outlet pressure and temperature when the system is running than measure those values at stand still in order to determine the presence of any non condensables.

SteinarN
29-02-2008, 01:00 AM
We can do some more reasoning in the above example.

If we add 2,5 litres (roughly 2,5 kg) refrigerant to the system, then the gas volume of the receiver will be reduced to 2,5 litres. Those 10 litres of non condensables would result in a 4 bar (10 litres gas compressed to 2,5 litres give a pressure of 4 bar) additional pressure above the saturated liquid pressure at receiver outlet. Thus adding additional refrigerant, above when there is sufficient refrigerant in the system to get a clear sight glass, will lead to increased condensing pressure and increased liquid subcooling in a system with noncondensables in it.

If there was no non condensables in the system, then there would not be any increase in the condensing pressure before the receiver got completely filled up.

Gary
29-02-2008, 01:19 AM
The correct way to determine any existence of non condensables is to measure the liquid subcooling at condenser outlet or receiver outlet. Assuming only minor hight differences and not any measurable pressure differences between condenser/receiver and not overfilled system there should be no measurable subcooling at condenser/receiver outlet. Any subcooling here is a certain symtom of non condensables in the system.


Sorry, but it doesn't work that way. On any system, if there is sufficient refrigerant to clear the sightglass, or even with an occasional bubble, there will be substantial subcooling at the receiver outlet.

SteinarN
29-02-2008, 01:39 AM
Sorry, but it doesn't work that way. On any system, if there is sufficient refrigerant to clear the sightglass, or even with an occasional bubble, there will be substantial subcooling at the receiver outlet.


Thats not my experience. At all my systems there is a very close relationship between the receiver pressure and the outlet temperature. I have had some transport refrigeration units with large subcooling, lets say 10 degres C. I have vacumed and filled new refrigerant and the subcooling has disapeared AND the condensing pressure got substantially reduced.

How du you explain that a bubble of warm and pure refrigerant gas can exist in the liquid pipe sorrounded by substantially subcooled liqiud :confused::confused:. If there was such a bubble it would very quicly lose its latent heat to the sorrounding cool liquid and dissapear completely. If there is any measurable substantly subcooling at the receiver outlet, then it is either non condensables in the receiver or there is an other refrigerant mix in the system than it should be.

Gary
29-02-2008, 01:54 AM
How du you explain that a bubble of warm and pure refrigerant gas can exist in the liquid pipe sorrounded by substantially subcooled liqiud :confused::confused:.


The same way I would explain droplets of liquid in a superheated suction line. The refrigerant is moving and there is carryover. If this were not true, we would only need 1 degree of superheat at the compressor inlet to ensure a solid flow of vapor.

SteinarN
29-02-2008, 02:19 PM
The same way I would explain droplets of liquid in a superheated suction line. The refrigerant is moving and there is carryover. If this were not true, we would only need 1 degree of superheat at the compressor inlet to ensure a solid flow of vapor.


I didnt realy see an answer to my question.

If there is sufficient liquid in the receiver to completely cover the inlet of the outlet tube, so that none of the gas in the receiver can enter the outlet tube, where does the ocasional bubbles in the sightglas come from?

Do you agree that any gaseous refrigerant, sorrounded by liquid subcooled refrigerant, must have a higher temperature than the sorrunding subcooled liquid?

How can any of the liquid subcooled refrigerant, drawn from the receiver, produce any gaseous refrigerant, visible in the sightglas, without any measurable pressure drop or any heat supplied?

This is the essence of the whole refrigeration process, that the temperature and the pressure of the refrigerant determines the possible states that same refrigerant can be in.

Gary
29-02-2008, 04:27 PM
The liquid in the receiver is subcooled. As it enters the tube, it is subcooled. If the liquid level barely covers the outlet tube, such that a bubble gets through occasionally, it is still subcooled.

Obviously, we are not going to agree on this. You will need to prove it to yourself by taking some measurements.

techie
29-02-2008, 04:41 PM
hey well sounds like it could be your filter drier could be partially blocked check the temp on either side of filter drier then check your expansion valve and orifice then try bring the discharge pressure to 250 psi and make sure the sight glass is full and stays full while doing it.check the amps pulling on your compressor to could be restriction or overcharged

SteinarN
29-02-2008, 05:09 PM
Obviously, we are not going to agree on this.


Seems that this is the only thing we agree on. We have a different understanding of the physics in a refrigeration system. I accept you have your understanding based on your experience and measurment you have done, but i have another understanding of the basics in a refrigeration system based on my knowlegde of physics and my experience and measurments i have done.

SteinarN
29-02-2008, 05:13 PM
hey well sounds like it could be your filter drier could be partially blocked check the temp on either side of filter drier then check your expansion valve and orifice then try bring the discharge pressure to 250 psi and make sure the sight glass is full and stays full while doing it.check the amps pulling on your compressor to could be restriction or overcharged


Our little "discussion" is about the fundamentals of a refrigeration system, not any spesific troubleshooting.

techie
29-02-2008, 05:16 PM
id say move the unit to where it can get proper ventilation and check your pressures then it could be that it not getting proper air circulation pressure must be on the high side between 220 and 290 psi comfortably jst because its set at 350 doesnt mean it must work at 350 350 is just a cut out however if its not cutting out at 350 then the pressure switch is stuffed

Gary
29-02-2008, 06:34 PM
Seems that this is the only thing we agree on. We have a different understanding of the physics in a refrigeration system. I accept you have your understanding based on your experience and measurment you have done, but i have another understanding of the basics in a refrigeration system based on my knowlegde of physics and my experience and measurments i have done.

This is not something I have pulled out of my hat. I have invested an enormous amount of research on a wide variety of systems, regarding this very point.

What I have found is that the sight glass clears at 10-15F subcooling, depending upon the velocity of the refrigerant flow. If your experience tells you otherwise, then it is what it is, and we can only agree to disagree.

Gary
29-02-2008, 06:36 PM
Our little "discussion" is about the fundamentals of a refrigeration system, not any spesific troubleshooting.

Uhhh... Actually, we are having a side discussion about fundamentals. The main thread is in fact about troubleshooting a specific system. :)

SteinarN
29-02-2008, 06:48 PM
Uhhh... Actually, we are having a side discussion about fundamentals. The main thread is in fact about troubleshooting a specific system. :)


Well, i have to give you right about that. Guess i got a bit engaged :)

But that is the only thing i give you right about ;)

Gary
29-02-2008, 06:53 PM
Here is something to ponder:

Static gas laws tell us that you can't have superheat in the presence of liquid, nor subcooling in the presence of vapor.

Place a half full container of refrigerant on a block of ice, with a heating pad on top. We now have superheated vapor at the top, subcooled liquid on the bottom and saturation at the vapor/liquid interface... all in the presence of each other.

How would you explain this?

The Viking
29-02-2008, 08:25 PM
Steinar/Gary,

I do find the discussion interesting.
From previous post I know Gary's definition of sub-cooling.
But Steinar, can you just confirm that we are talking about saturated temperature of gas at pressure measured by gauge, less true measured temperature of gas?
If we agree on this then, unfortunately, I have to agree with Gary.....

SteinarN
29-02-2008, 08:44 PM
The superheated gas in the top of the bottle isnt in contact with the saturated liquid in the liquid/vapor interface. The more or less superheated gas in the middle of the bottle insulates the more superheated gas in the top.

The same applies to the liquid in the bottom which isnt in contact with the saturated liquid/vapor interface.

However there is a flow of heat from the warm gas down to the cool liquid. As soon as the heat/cool source is removed the temperatures will start to equalice and we end up with a saturated liquid/vapor mix in the end.

To take this reasoning a step further, we can substitute the bottle with an evaporator. We can se one cirque as a very narrow and long bottle. At the inlet of one cirque we have a saturated mix of liqiud and vapor coresponding to the liquid/gas interface in the bottle. At the outlet of the cirque we have (normaly) superheated gas, coresponding to the top of the bottle. The same applies in a condenser.

I cant se any problem with containing superheated gas and subcooled liquid in the same chamber as long as we supply and/or remove heat as we do in an evaporator and a condenser. If no heat is added or removed, then we will end up with saturated gas/liquid.

SteinarN
29-02-2008, 08:57 PM
Steinar/Gary,

I do find the discussion interesting.
From previous post I know Gary's definition of sub-cooling.
But Steinar, can you just confirm that we are talking about saturated temperature of gas at pressure measured by gauge, less true measured temperature of gas?
If we agree on this then, unfortunately, I have to agree with Gary.....

I didnt catch the meaning of your question :o
English isnt my native language.

Saturated temperature of gas at pressure measured by gauge, less true measured temperature of gas gives the subcooling of the gas :confused::confused:

However:
Saturated temperature of liquid at pressure measured by gauge, less true measured temperature of liquid give the subcooling of the liquid.

And:
True temperature of gas less saturated temperature of gas measured by gauge gives the superheat of the gas.

nike123
29-02-2008, 09:09 PM
SteinarN, you (and any one interested) should go here
http://hvac-talk.com/vbb/showthread.php?t=56495
and read whole thread. I just reading it and it seems that could give us some answers.

SteinarN
29-02-2008, 09:29 PM
SteinarN, you (and any one interested) should go here
http://hvac-talk.com/vbb/showthread.php?t=56495
and read whole thread. I just reading it and it seems that could give us some answers.

17 pages :eek:

It take days to read it.

On page 3 now. :cool:

SteinarN
29-02-2008, 09:50 PM
From that link i see one instance where we can have substantly subcooled liquid from the receiver. That is in the case of a hotgas by-pass valve delivering hotgass directly into the top of the receiver in order to maintain condensing pressure in cold ambient. That hot gass will maintain pressure in the receiver and displace a portion of the refrigerant into the condenser in a similar facion as non condensables will do. Thereby a large portion of the end of the condenser will contain liquid refrigerant, gradually acheive more subcooling towards the condenser outlet. The liquid will loose some of its subcooling when it enters the receiver and receives some heat from the warm gas there but still maintain substantly subcooling at the receiver outlet. But this requires a constant supply of hot gas into the receiver.

Gary
29-02-2008, 10:26 PM
SteinarN, you (and any one interested) should go here
http://hvac-talk.com/vbb/showthread.php?t=56495
and read whole thread. I just reading it and it seems that could give us some answers.

An interesting discussion for sure. There are few people in this industry I would consider to be true authorities and Andy Schoen is one of them.

frank
29-02-2008, 10:51 PM
There are few people in this industry I would consider to be true authorities and Andy Schoen is one of them.
AKA - Prof Sporlan ?

Gary
01-03-2008, 12:09 AM
AKA - Prof Sporlan ?

Yep... haven't seen him posting lately...

Gary
01-03-2008, 01:03 AM
17 pages :eek:

It take days to read it.

On page 3 now. :cool:

On page 16, near the bottom, Andy states that subcooling is not needed on systems with large receivers. Perhaps this explains the differences in our experiences.

In my books, I tell people to charge a TXV system to a clear sight glass or 15F/8.5K subcooling, whichever comes first. I'm thinking that covers it. :)

nike123
01-03-2008, 01:11 AM
In my books, I tell people to charge a TXV system to a clear sight glass or 15F/8.5K subcooling, whichever comes first. I'm thinking that covers it. :)

Is that subcooling same with low ambient and low load condition as with high ambient and high load condition.
Or, do we need to charge when one of these extremes is satisfied.
__________________

US Iceman
01-03-2008, 03:54 AM
On page 16, near the bottom, Andy states that subcooling is not needed on systems with large receivers.


To be honest I have not read the whole thread on the other site, but I question a blanket statement like this. If you have liquid rising up to the TXV's you will need subcooling no matter what size the receiver is.

On the other hand, if you have head pressure controls and flooded condensers in the winter time you have more than enough subcooling for almost anything you want to do.

Personally, I do not like blanket statements at all without defining the parameters on which they apply. It is the same danger as using rules of thumb for everything when they only apply to limited circumstances.

The subject of subcooling keeps coming up in different threads and I think we need to keep in mind the two ways subcooling is created.

One is the traditional way in which the liquid refrigerant is cooled below it's saturation temperature. In this case you have an actually lowered the refrigerant temperature but not it's pressure.

The other is when the liquid pressure is increased above the pressure equal to the saturation point the liquid exists at before the additional pressure is applied. In this case you have increased the pressure of the liquid but not changed it's temperature.

The entire discussion is based on one of the above and the specific conditions encountered in the system.;)

Gary
01-03-2008, 05:33 AM
Oops... I misquoted Andy. What he said was that condenser subcooling was not needed on systems with large receivers. I would take that to mean subcooling in the drop leg between condenser and receiver.
.

Gary
01-03-2008, 05:46 AM
The subject of subcooling keeps coming up in different threads and I think we need to keep in mind the two ways subcooling is created.

One is the traditional way in which the liquid refrigerant is cooled below it's saturation temperature. In this case you have an actually lowered the refrigerant temperature but not it's pressure.

The other is when the liquid pressure is increased above the pressure equal to the saturation point the liquid exists at before the additional pressure is applied. In this case you have increased the pressure of the liquid but not changed it's temperature.


Yes, lowering liquid temperature is good subcooling, raising saturated condensing temperature is bad subcooling, keeping in mind that subcooling is the difference between these two. :)

In any case, to get back to the original point, subcooling does not necessarily indicate non-condensables even if it is excessive subcooling. Excessive subcooling is more likely an indication of overcharge, although it might (less likely) indicate non-condensables.

Gary
01-03-2008, 06:05 AM
To get back to the subject of this thread, even though we don't know what the actual subcooling temperature is, we know that the TD is 14K/25F, which is not even close to being excessive and therefore the subcooling is highly unlikely to be excessive, whether from overcharge or non-condensables.

US Iceman
01-03-2008, 07:13 AM
...subcooling does not necessarily indicate non-condensables even if it is excessive subcooling.


Almost, but... doing the calculations with the temperature and pressure readings can cause the two (subcooling or non-condensables) to be interpreted as or appear to be the same thing.

This is a difficult thing for people to accept because the only way to prove it is have a connection on the condenser drain.

If you open the connection and liquid refrigerant comes out, you have subcooling.

If you open the connection and vapor bleeds out, you have non-condensables.



...raising saturated condensing temperature is bad subcooling...


I quite agree. Dan mentioned this once before as one possible effect.

But you have to remain aware that pressure can be increased by other means also. A refrigerant pump is one way. Another is static head in liquid!

PH charts are the way to follow this, or vapor pressure curves for the refrigerant in question. You can do this is with pressure/temperature tables also but the lack of reference lines make it less apparent.

Refrigerologist
04-03-2008, 10:52 PM
The correct way to determine any existence of non condensables is to measure the liquid subcooling at condenser outlet or receiver outlet. Assuming only minor hight differences and not any measurable pressure differences between condenser/receiver and not overfilled system there should be no measurable subcooling at condenser/receiver outlet. Any subcooling here is a certain symtom of non condensables in the system.

When there is sufficient refrigerant in the system, any non condensables will accumulate in the receiver bc only liquid is drawn out of the receiver and the non condensables (gasses) cant find the way to the bottom of the receiver where the outlet pipe is.

An example:
Lets say the liquid temperature (condenser outlet and receiver outlet) is 30 degres C, but you measure a condensing/receiver pressure of 15,1 bar. At 30 condensing/liquid outlet, the pressure should have been 13,1 bar! In this instance you have 2 bar additional pressure (15,1-13,1) in the receiver caused by non condensables. Lets say the gas phase volume of the receiver is 5 litres, then you have 10 litres of noncondensables at atmospheric pressure in the system. (10 litres at 1 atmosphere equals 5 litres at those 2 atmospheres additional pressure.) This is assuming that the temperature of the liquid surface in the receiver is the same temperature as the condenser outlet/receiver outlet. This assumtion should be valid in a system with short pipes between condenser and receiver, not any excess pressure loss between condenser outlet and receiver outlet and not considerably temperature difference between the condensing temperature and the surrounding air of the receiver.

When the system is stopped, the non condensables have a possibility to escape from the receiver and expand/dilute into a much larger volume of the system. That 10 litres of non condensables, when expanded/diluted in, lets say, 20 litres of the system, will cause an additional pressure above the saturated pressure of only 0,5 bar. (10 litres at 1 bar equals 20 litres at 0,5 bar) Thus it is far more accurate to measure the receiver outlet pressure and temperature when the system is running than measure those values at stand still in order to determine the presence of any non condensables.

I cannot agree with your statement. Non condensables accumulate at the top of the condenser. These non condensibles take up room that is normally used in cooling the superheated refrigerant. Therefore the condenser is effectively smaller and there will be little or no subcooling or worse still the refrigerant will remain superheated.
Tol check for non condensibles you must fit your gauges, switch the system off and allow the equipment to reach the average ambient. Read the pressure and compare for a saturated pressure given for that ambient. If it is 14.7lbs above that expected then air is present.

Refrigerologist
04-03-2008, 10:57 PM
To make things clear an overcharge of refrigerant will increase the amount of sub-cooling of the liquid at the liquid line. Non-condenables will reduce sub-cooling at the liquid line for reasons that are set out in my last post. These are facts and not assumptions!

Refrigerologist
04-03-2008, 11:03 PM
To make things even clearer: Think about a dirty condenser. The condenser efficiency is lowered. It is made for all intensts and purposes too small for the job. Non-condenables do the same thing as they take up room in the condenser and CANNOT BE CONDENSED, THINK ABOUT IT! Therfore the non-condensables effectively make the condenser smaller by occupying space that the refrigerant should be using to be cooled. The air is NOT driven out of the condenser, it remains where it is trapped at the top!

Refrigerologist
04-03-2008, 11:09 PM
Another point I should make is that a system is not necessarily fully charged because it has a full sight glass. The liquid line temperature should be checked to ascertain the actual amount of sub-cooling. Many times it is necessary to add further refrigerant to a system, even though the sight glass is clear. Try it some time phone a chiller manufacturer and find out their recommended sub-cooling figures. Then if you are having to recharge or commission a system you may find that by charging only to a full sight glass the amount of sub-cooling is higher that which is recommended.

Refrigerologist
04-03-2008, 11:15 PM
On page 16, near the bottom, Andy states that subcooling is not needed on systems with large receivers. Perhaps this explains the differences in our experiences.

In my books, I tell people to charge a TXV system to a clear sight glass or 15F/8.5K subcooling, whichever comes first. I'm thinking that covers it. :)

Gary I never read this post, but yes you have hit it in a nutshell. Systems should be charged to the sub-cooling value of refrigerant at the liquid line. Sight glasses are only a guide o what is happening.

As for some of these other posts, I cannot believe what I am reading!

US Iceman
04-03-2008, 11:38 PM
As for some of these other posts, I cannot believe what I am reading!


I guess it depends on which ones you are reading.;)

You can't make broad statements and expect them to hold true for every case.



Non condensables accumulate at the top of the condenser.


Not all the time. I have modified my answer in this edit.

SteinarN is getting to the heart of the problem. Where the non-condensables appear also depends on how the condensers are piped. If you have a liquid seal (P-trap) in the condenser drain line the non-condensables get trapped on top of the liquid seal. If the liquid seal disappears or the drain line is not trapped at all, the non-condensbales do flow down into the receiver. That makes a lot more sense!

SteinarN
04-03-2008, 11:45 PM
To make things clear an overcharge of refrigerant will increase the amount of sub-cooling of the liquid at the liquid line. Non-condenables will reduce sub-cooling at the liquid line for reasons that are set out in my last post. These are facts and not assumptions!


In a normal fin and tube condenser, the non condensibles will acumulate in the receiver. The refrigerant is flowing through the tubes in the condenser at maybe 1-3 m/s. How can the non condensables molecules know they shall apply emergency brakes in order to not be sweept along with the refrigerant gas and liquid towards the outlet of the condencer?

The non condensibles will acumulate in the receiver, adding additional part pressure in the receiver, thereby restrict the exit of refrigerant out of the condenser. The result is that the end of the condenser will be full of liquid refrigerant gradually acheiving substantly subcooling towards the outlet of the condenser. Condensing pressure will rise as well.

SteinarN
05-03-2008, 12:06 AM
Another point I should make is that a system is not necessarily fully charged because it has a full sight glass. The liquid line temperature should be checked to ascertain the actual amount of sub-cooling. Many times it is necessary to add further refrigerant to a system, even though the sight glass is clear. Try it some time phone a chiller manufacturer and find out their recommended sub-cooling figures. Then if you are having to recharge or commission a system you may find that by charging only to a full sight glass the amount of sub-cooling is higher that which is recommended.

I always install receivers with sight glass at the bottom and if available at the top also. Then i have an exelent supervision of the actual refrigerant level in the system. When i charge the system, i charge until the ball in the lower sight glass floats. At that point i have a clear liquid line sight glass, or maybe with an ocasional bubble. If i should charge until i got a subcooling of lets say 5C at condenser or receiver outlet, i would have to charge the receiver completely full. I dont care of the subcooling as long as i have liquid some way up from the bottom in the receiver.

Some says the proper amount of subcool is, lets say 8C. If i design a system with a dt condenser at 8K, how can it be possible to acheive a subcooling of 8C?

I have several systems with floating head running with condenser dt as low as 5K in low load condition. What is your recomended subcooling in such a case?

SteinarN
05-03-2008, 12:38 AM
I guess it depends on which ones you are reading.;)

You can't make broad statements and expect them to hold true for every case.



Not all the time. I have modified my answer in this edit.

SteinarN is getting to the heart of the problem. Where the non-condensables appear also depends on how the condensers are piped. If you have a liquid seal (P-trap) in the condenser drain line the non-condensables get trapped on top of the liquid seal. If the liquid seal disappears or the drain line is not trapped at all, the non-condensbales do flow down into the receiver. That makes a lot more sense!

Thank you for some support :)

I felt i was taken on heavily.

I agree in what you said about liquid seal. I'm not into the industrial stuff. I dont know anything about the construction of the condensers there. I'm talking about normal comercial fin and tube condensers.

Older condensers had larger diameter tubes and consequently lower pressure drop and lower refrigerant speed in the tubes. If the ricers? also had a large diameter, then i can imagine some non condensibles accumulate in the condenser.

However, with new modern designed high efficiency condensers the tubes has a much smaller diameter and consequently larger refrigerant speed through the tubes. Also the ricers is smaller. This makes it next to impossible for any non condensables to accumulate in the condenser. When i design the liqiud line i aim for a refrigerant speed of roughly 1,5m/s. With such speed i doubt any non condensables can avoid beeing swept along to the receiver regardless of any traps or the direction of the liqiud pipe.

Gary
05-03-2008, 12:39 AM
Obviously, the subcooling cannot exceed the TD, but rarely are TD's that low. The exception does not invalidate the principle.

SteinarN
05-03-2008, 12:53 AM
Obviously, the subcooling cannot exceed the TD, but rarely are TD's that low. The exception does not invalidate the principle.

It was not you Gary that i defended my self against. It was Refrigerologist.

But that said, when i design a system, i design it with no more than 10K dt condensing at full load summer time. The additional cost for a larger condenser is saved back in a couple years due to lower power consumption to the compressor. In some cases i can get away with the next smaller compressor also. The actual load at night and with low humidity for instance is easily only 50% of full design load. Thereby a dt of only 5K.

Gary
05-03-2008, 12:59 AM
Just to make sure we are on the same page:

Condenser dT is air out minus air in.

Condenser TD is saturated condensing temperature (SCT) minus air in.

SteinarN
05-03-2008, 01:05 AM
Just to make sure we are on the same page:

Condenser dT is air out minus air in.

Condenser TD is saturated condensing temperature (SCT) minus air in.

Ahhh. Seems that we have some different abbreviations on oposite sides of the Atlantic ;)

I'm talking about TD. SCT minus air in.

Gary
05-03-2008, 01:05 AM
It was not you Gary that i defended my self against. It was Refrigerologist.


You should not feel that you are under attack. We are simply discussing an important aspect of our trade. Don't take it personally.

Gary
05-03-2008, 01:11 AM
There seems to be a great deal of confusion on both sides of the pond. :)

Throughout the scientific world, a delta-T (dT) is a change in temperature of a single substance or flow of substance, while a TD is a temperature difference between two different substances or flows of substances.

SteinarN
05-03-2008, 01:15 AM
You should not feel that you are under attack. We are simply discussing an important aspect of our trade. Don't take it personally.

Maybe i owe you to attack me some time :D

But i did actually feel i had to defend my self against Refrigerologist. But now i have don it :)

And yes, it is very interesting to discuss various aspects of our trade. I apreciate very much when i get substantiated answers. I do get respect (not to much tho) for people with a high grade of knowlegde. I know i maybe appear stubborn sometimes, but i hope you guys in here can take me down if i get to stubborn :)

SteinarN
05-03-2008, 01:19 AM
There seems to be a great deal of confusion on both sides of the pond. :)

Throughout the scientific world, a delta-T (dT) is a change in temperature of a single substance or flow of substance, while a TD is a temperature difference between two different substances or flows of substances.

Hmmmm. I use delta T as a difference in temp of a single substance as you says. But i think that delta T is also used in catalogs here in Norway for the difference of SCT and entering air of condensers and evaporators also. Have to have a look tomorrow for sure.

Gary
05-03-2008, 01:47 AM
I have several systems with floating head running with condenser dt as low as 5K in low load condition. What is your recomended subcooling in such a case?

In low ambient conditions, if there is no fan control and the SCT is below 90F/32C, I block off part of the condenser, raising the SCT to about 100F/38C before checking subcooling and superheat. I would do the same on a floating head system.

I would not consider 15F/8.5K to be the norm for receiver outlet subcooling, but rather an upper limit, beyond which liquid is backing up into the condenser... and I always recommend charging until the sight glass is clear or this limit is reached, whichever comes first... whatsmore I always check superheat before charging, as it is a mistake to add refrigerant if the superheat is low.

US Iceman
05-03-2008, 04:14 AM
I agree in what you said about liquid seal. I'm not into the industrial stuff. I dont know anything about the construction of the condensers there. I'm talking about normal commercial fin and tube condensers.


Normal for me is the big evaporative condensers and thousands of pounds of ammonia.;)

One of the good things that came out of this discussion is the fact that each industry has it's own unique requirements, although they are based on common physics.

Air cooled systems do not normally have equalizing lines between the condenser and receiver, so everything flows by pressure difference alone essentially.

On ammonia systems the receiver is a basic gravity drain with the receiver pressure equalizing with the discharge pressure. This would require much larger pipes (risers) as we try to design these so the condenser does not have liquid backed up in it for subcooling. Why use condensing heat transfer surface for subcooling???

These simple differences dictate some different piping practices also, so what happens in a "*****" system may be somewhat different than an ammonia system.

Several other points about non-condensables, subcooling, etc were also discussed. I hope everyone reading this thread can follow it since we covered so many related topics.;)

BTW, you were not alone in the thread. I was watching the discussion for awhile.:D

Tesla
05-03-2008, 08:40 AM
Guys the methods of measurement described in threads is old hack and just an estimated guess. There is only one correct way to measure the gas - that is direct temp and press measurement. There is a tool from yellow jacket ritchie which does this and I think a lesser one from robinare. So the old way of measuring the pipe temp is not accurate.

SteinarN
05-03-2008, 08:53 AM
Guys the methods of measurement described in threads is old hack and just an estimated guess. There is only one correct way to measure the gas - that is direct temp and press measurement. There is a tool from yellow jacket ritchie which does this and I think a lesser one from robinare. So the old way of measuring the pipe temp is not accurate.

Actually i have that kit, two of them. :)

I plan to do some serious testing soon. Insert that
thermometer into the scrader on the receiver outlet rotalock valve and measure the exact pressure at the same time.

Wonder if i should soften my position ever so slightly first. Admit it may be a slight degree of subcooling there :D

Have to take some pictures as vell. Just for the records. :)

Josip
05-03-2008, 02:48 PM
Hi, Mike :)


Normal for me is the big evaporative condensers and thousands of pounds of ammonia.;)

....for me too .....btw...with compressor's electrical motor usually bigger of 100kW:D


Best regards, Josip :)

nike123
05-03-2008, 03:46 PM
Hi, Mike :)



....for me too .....btw...with compressor's electrical motor usually bigger of 100kW:D


Best regards, Josip :)
Womans said, that size is not only thing what is matter! ;):D

Springbok
05-03-2008, 03:55 PM
Hey chilltechnician,since you were the original poster of this thread,does this answer your questions?:D

SteinarN
05-03-2008, 11:02 PM
Hi, Mike :)



....for me too .....btw...with compressor's electrical motor usually bigger of 100kW:D


Best regards, Josip :)


The largest system i have had a look at was on some sort of a trawler, i dont know the english word, they fished pelagic fish, like herring. They take large amounts aboard in a short time, lets say 100 ton fish plus 100 ton water. Or maybe it was several hundred tons, i dont remember. Then that mass must be chilled down from sea temperature of maybe 8C to close to 0C in no more than a couple hours. This was a smal boat but they had a system with 2 large screws with combined cooling capasity of 1950 kW. The electric generator delivered some 2000 kW. The system was actually rather simple. But it was very interesting to have a close look at it and se it running.

Gary
05-03-2008, 11:40 PM
The largest system I worked on was a 3600 ton/12660 kW centrifugal chiller for a skyscraper. You could walk around on the top of the motor. They had 3 of those and a little 1250 ton/4400 kW. We had to notify the power company two weeks in advance before starting any of these, so they could divert power for it.

ChillTechnican
07-03-2008, 09:43 AM
Yes , well that all brought up a few things to think about and yes my question has been answered , thanks to all. i now own a MA Line dual probe thermometer , and it has been really useful from day one and i am now confident that i am getting accurate readings and there fore a much clearer idea of what the system is doing.
cheers guys and look forward to getting info when i next have a question.
i hope to get back to the chiller in question next week for relocation, will take readings again and let you know.:)

ChillTechnican
07-03-2008, 09:44 AM
the weather here has been alot cooler this last 10 days and had no problems!

Refrigerologist
08-03-2008, 02:36 AM
The correct way to determine any existence of non condensables is to measure the liquid subcooling at condenser outlet or receiver outlet. Assuming only minor hight differences and not any measurable pressure differences between condenser/receiver and not overfilled system there should be no measurable subcooling at condenser/receiver outlet. Any subcooling here is a certain symtom of non condensables in the system.

When there is sufficient refrigerant in the system, any non condensables will accumulate in the receiver bc only liquid is drawn out of the receiver and the non condensables (gasses) cant find the way to the bottom of the receiver where the outlet pipe is.

An example:
Lets say the liquid temperature (condenser outlet and receiver outlet) is 30 degres C, but you measure a condensing/receiver pressure of 15,1 bar. At 30 condensing/liquid outlet, the pressure should have been 13,1 bar! In this instance you have 2 bar additional pressure (15,1-13,1) in the receiver caused by non condensables. Lets say the gas phase volume of the receiver is 5 litres, then you have 10 litres of noncondensables at atmospheric pressure in the system. (10 litres at 1 atmosphere equals 5 litres at those 2 atmospheres additional pressure.) This is assuming that the temperature of the liquid surface in the receiver is the same temperature as the condenser outlet/receiver outlet. This assumtion should be valid in a system with short pipes between condenser and receiver, not any excess pressure loss between condenser outlet and receiver outlet and not considerably temperature difference between the condensing temperature and the surrounding air of the receiver.

When the system is stopped, the non condensables have a possibility to escape from the receiver and expand/dilute into a much larger volume of the system. That 10 litres of non condensables, when expanded/diluted in, lets say, 20 litres of the system, will cause an additional pressure above the saturated pressure of only 0,5 bar. (10 litres at 1 bar equals 20 litres at 0,5 bar) Thus it is far more accurate to measure the receiver outlet pressure and temperature when the system is running than measure those values at stand still in order to determine the presence of any non condensables.

Please refer to Daltons Law regarding gas pressure. You will see that different gases excert their own partial pressure. Therefore, if any air is present in a closed system, that has been switched off and allowed to cool down or warm up to the ambient temperature, then by consulting your saturated refrigerant pressure/temperature relationship chart for that refrigerant if the pressure is 1bar or 14.7lbs per sq in higher then it must contain air.

Refrigerologist
08-03-2008, 02:47 AM
Why do we need sub-coolinmg then? Firstly it increases the refrigerating effect by reducing adibiatic expansion after the expansion device. Secondly it ensures that there is no flashing of the liquid refrigerant to vapour in the liquid line due to pressure drop within the line. Therefore Gary must be correct that sub-cooling is a good thing and it is what manufacturer's do ask for and they design their condensers specifically for it, hence many condensers actually have a sub-cooler coil.

Refrigerologist
08-03-2008, 01:18 PM
The correct way to determine any existence of non condensables is to measure the liquid subcooling at condenser outlet or receiver outlet. Assuming only minor hight differences and not any measurable pressure differences between condenser/receiver and not overfilled system there should be no measurable subcooling at condenser/receiver outlet. Any subcooling here is a certain symtom of non condensables in the system.

When there is sufficient refrigerant in the system, any non condensables will accumulate in the receiver bc only liquid is drawn out of the receiver and the non condensables (gasses) cant find the way to the bottom of the receiver where the outlet pipe is.

An example:
Lets say the liquid temperature (condenser outlet and receiver outlet) is 30 degres C, but you measure a condensing/receiver pressure of 15,1 bar. At 30 condensing/liquid outlet, the pressure should have been 13,1 bar! In this instance you have 2 bar additional pressure (15,1-13,1) in the receiver caused by non condensables. Lets say the gas phase volume of the receiver is 5 litres, then you have 10 litres of noncondensables at atmospheric pressure in the system. (10 litres at 1 atmosphere equals 5 litres at those 2 atmospheres additional pressure.) This is assuming that the temperature of the liquid surface in the receiver is the same temperature as the condenser outlet/receiver outlet. This assumtion should be valid in a system with short pipes between condenser and receiver, not any excess pressure loss between condenser outlet and receiver outlet and not considerably temperature difference between the condensing temperature and the surrounding air of the receiver.

When the system is stopped, the non condensables have a possibility to escape from the receiver and expand/dilute into a much larger volume of the system. That 10 litres of non condensables, when expanded/diluted in, lets say, 20 litres of the system, will cause an additional pressure above the saturated pressure of only 0,5 bar. (10 litres at 1 bar equals 20 litres at 0,5 bar) Thus it is far more accurate to measure the receiver outlet pressure and temperature when the system is running than measure those values at stand still in order to determine the presence of any non condensables.

I am not attacking you personally, just having a debate. I think we all need to go back to the fundamentals: The compressor should not be thought of as a pump. It draws vapour from the evaporator, compresses it, and adds heat, by friction. This superheated gas enters the condenser and by being cooled in the first third (approx) of the condenser it is desuperheated. In the next third it begins to condense. (When I was at Willesden Tech, circa. 1975, they had a fully operable glass tube fridge system and you could actually see this condensation taking place, it was more like rain). At this point any non-condensibles due to the density being lower than the liquid refrigerant rises back to the top of the condenser and remains trapped. The refrigerant carries on being cooled/sub-cooled. The liquid refrigerant carries on as normal, to, (if fitted the receiver), and then on to the expansion device. Remember that the liquid refrigerant is a medium temperature subcooled liquid at this point and due to the pressure differential, which is created by the expansion device, and the compressor withdrawing the vapour, and compressing it, is forced into the evaporator where its' pressure drops. The compressor draws the vapourized refrigerant back into its' bores to be compressed and the temperature is raised. And so the cycle continues. You need to visulize what is occuring in the condenser: the superheated gas does not just flow through and collect any air pushing it in front. As the refrigerant condenses, the air is released and returns to the top of the condenser taking up valuable room. This is why it is called non-condensibles. If the air were to condense it would be carried around the system in a continual cycle. I hope that this rather poor description helps.

In order to clarify some of the above, if a cylinder of refrigerant were piped to an open ended evaporator via a simple capilliary expansion device, and the liquid valve opened, then liquid refrigerant would pass though capilliary and as in a closed system refrigeration would take place. Obviously an expensive excercise! The compressor and condenser arrangement is used to complete the cycle and to retain the refrigerant. Remember we do not need a compressor to obtain refrigeration, we can use absorbtion systems where the initial driving force is heat. Both systems use the application of energy to operate the cycle.

You are correct on one point though if the discharge pressure has risen due to the presence of non-condensibles it is possible to have sub-cooling. But the refrigerant would be at a higher temperature than would be normal for a given ambient. I had not actually thought that part through. Conversely, if there is enough air present and full condensation cannot be acheived then it is possible that there would be no sub-cooling.

SteinarN
08-03-2008, 02:05 PM
Please refer to Charles Law and Boyles Law regarding gas pressure. You will see that different gases excert their own partial pressure. Therefore, if any air is present in a closed system, that has been switched off and allowed to cool down or warm up to the ambient temperature, then by consulting your saturated refrigerant pressure/temperature relationship chart for that refrigerant if the pressure is 1bar or 14.7lbs per sq in higher then it must contain air.

I'm fully avare of the part pressures from different gasses in a closed system. There is no need for the pressure in a closed system to be 1bar higher than the saturated temperature if it is air in the system. A smal amount of air will increase the pressure less than one bar, lets say 0,1bar while a large amount of air will increase the pressure several bar over the saturated pressure.

A system containing a smal amount of air will show a far less increase in the saturated pressure at standstill than will be the case if the air could be collected in a smal part of the system like the receiver. Hence my sugestion on how to establish the eventual presence of air in the system.

SteinarN
08-03-2008, 02:17 PM
Why do we need sub-coolinmg then? Firstly it increases the refrigerating effect by reducing adibiatic expansion after the expansion device. Secondly it ensures that there is no flashing of the liquid refrigerant to vapour in the liquid line due to pressure drop within the line. Therefore Gary must be correct that sub-cooling is a good thing and it is what manufacturer's do ask for and they design their condensers specifically for it, hence many condensers actually have a sub-cooler coil.

I have never argued subcooling isnt a good thing. I'm fully avare of and i'm able to calculate the result in detail of the "free" increase in cooling capasity if the condenser outlet temperature is lowered or alternatively the receiver outlet is routed through a subcooling coil.

On the other hand, subcooling caused by an increase in condensing pressure without actually lower the liquid temperature is a loss no matter how large the resulting subcooling is.

SteinarN
08-03-2008, 02:46 PM
I am not attacking you personally, just having a debate. I think we all need to go back to the fundamentals: The compressor should not be thought of as a pump. It draws vapour from the evaporator, compresses it, and adds heat, by friction. This superheated gas enters the condenser and by being cooled in the first third (approx) of the condenser it is desuperheated. In the next third it begins to condense. (When I was at Willesden Tech, circa. 1975, they had a fully operable glass tube fridge system and you could actually see this condensation taking place, it was more like rain). At this point any non-condensibles due to the density being lower than the liquid refrigerant rises back to the top of the condenser and remains trapped. The refrigerant carries on being cooled/sub-cooled. The liquid refrigerant carries on as normal, to, (if fitted the receiver), and then on to the expansion device. Remember that the liquid refrigerant is a medium temperature subcooled liquid at this point and due to the pressure differential, which is created by the expansion device, and the compressor withdrawing the vapour, and compressing it, is forced into the evaporator where its' pressure drops. The compressor draws the vapourized refrigerant back into its' bores to be compressed and the temperature is raised. And so the cycle continues. You need to visulize what is occuring in the condenser: the superheated gas does not just flow through and collect any air pushing it in front. As the refrigerant condenses, the air is released and returns to the top of the condenser taking up valuable room. This is why it is called non-condensibles. If the air were to condense it would be carried around the system in a continual cycle. I hope that this rather poor description helps.

In order to clarify some of the above, if a cylinder of refrigerant were piped to an open ended evaporator via a simple capilliary expansion device, and the liquid valve opened, then liquid refrigerant would pass though capilliary and as in a closed system refrigeration would take place. Obviously an expensive excercise! The compressor and condenser arrangement is used to complete the cycle and to retain the refrigerant. Remember we do not need a compressor to obtain refrigeration, we can use absorbtion systems where the initial driving force is heat. Both systems use the application of energy to operate the cycle.

You are correct on one point though if the discharge pressure has risen due to the presence of non-condensibles it is possible to have sub-cooling. But the refrigerant would be at a higher temperature than would be normal for a given ambient. I had not actually thought that part through. Conversely, if there is enough air present and full condensation cannot be acheived then it is possible that there would be no sub-cooling.

I've never seen a glass tube condenser. One thing that comes to mind is that such a condenser without fins must have an exceptional low capasity in relation to the area of pipe surface and pipe volume. It makes sence for me that the gas has to flow very slowly through the pipe and therefore show the liquid at the bottom and gas at the top in the pipe.

In a real modern condenser the speed of flow is much greater and not allowing that separation of the gas and liquid as you saw. The flow inside a real condenser is more like the flow through a liquid line sight glass on a system short of gas where the sight glass is showing heavy foaming, a relatively uniform flow of opaque foam.

In the beginning of the condensing section there is the highest velocity. There will be a thin film of liquid at the pipe wall, and fast flowing gas in the rest of the pipe. As the liquid film grews thicker the gas will tear off excess liquid from the wall. There will gradually arise a gas/liquid foam at the center of the pipe but still a thin film of liquid at the wall. Toward the end the film at the wall grew thicker and actually partially start to subcool. The velocity decreases gradually as the foam in the middle condenses fully. Only in the very last part of the condenser is the velocity low enough to allow some separation of the liquid at the bottom and gas at the top in the pipe. However any noncondensables will be sweept along with the refrigerant out of the condenser.

Non condensables in the receiver will cause increased condensing pressure and lower condenser outlet temperature. You can acheive a fenomenal amount of subcooling with non condensables in the receiver. If it is enough refrigerant in the system, then it is absolutely impossible not to have subcooling out of the condenser with non condensables in the system.

Refrigerologist
08-03-2008, 06:45 PM
I'm fully avare of the part pressures from different gasses in a closed system. There is no need for the pressure in a closed system to be 1bar higher than the saturated temperature if it is air in the system. A smal amount of air will increase the pressure less than one bar, lets say 0,1bar while a large amount of air will increase the pressure several bar over the saturated pressure.

A system containing a smal amount of air will show a far less increase in the saturated pressure at standstill than will be the case if the air could be collected in a smal part of the system like the receiver. Hence my sugestion on how to establish the eventual presence of air in the system.

Not in a static system, it will only raise the pressure by 1 atmosphere, unless you have managed to compress the non-condensibles and the compressor kept sucking more and more air into the system and it became completely overload with air. Before that point is reached the system waould have failed on high pressure limit.
Switching the system off, allowing it to stabilse to the average ambient, and then reading the standing pressure and comparing the recorded pressure against a pressure temperature relationship chart for the refrigerant is standard industry practice, and the according to the laws of partial pressures the air will excert its own force ie 1 atmosphere above the refrigerant pressure. This is a scientific fact. I did not make it up and I am sure if you research it you will find it to be true!

Also you say the non condensibles end up in the receiver. Where do they go then in a system without a receiver?

I did also say that I had not thought it through and that subcooling could be high, but this would be based on the higher than normal pressure, but the actual refrigerant temperature would also be much higher than is usual due to the lack of condensing effect due to air remaining in the top of the condenser.

Refrigerologist
08-03-2008, 06:55 PM
Why not look up KOTZA on the internet and get one of their training evalution disks. It covers this subject really well. It is free and provides tests based on the temperature value and pressure readings and uses an animated type display showing gauges etc.

SteinarN
08-03-2008, 07:00 PM
Not in a static system, it will only raise the pressure by 1 atmosphere, unless you have managed to compress the non-condensibles and the compressor kept sucking more and more air into the system and it became completely overload with air. Before that point is reached the system waould have failed on high pressure limit.
Switching the system off, allowing it to stabilse to the average ambient, and then reading the standing pressure and comparing the recorded pressure against a pressure temperature relationship chart for the refrigerant is standard industry practice, and the according to the laws of partial pressures the air will excert its own force ie 1 atmosphere above the refrigerant pressure. This is a scientific fact. I did not make it up and I am sure if you research it you will find it to be true!

I dont se that any of what i said contradict what you says here. Of course if you charge refrigerant in a system while it contains one bar absolute pressure of air, the resulting pressure will be 1 bar higher than the saturated ref. pressure. But if it contained only, lets say, 0,1 bar absolute pressure of air, then the resulting saturated pressure would be 0,1 bar higher as you indicate. If that system is started and the air acumulate in the receiver, then the receiver/condensing pressure would be significantly more than 0,1 bar higher than the saturated pressure. Imo, small amounts of non condensibles is best diagnosed with the system running, especially in systems with small receiver volumes compared to the volume of the rest of the system.

Refrigerologist
08-03-2008, 07:54 PM
Sorry guys', in one of my previous posts I quoted the wrong gas law. It should of course been Daltons' Law of Partial Pressures. I have corrected it to save confusion, but mainly to stop me looking any more of a plonker than I some of you may already think!

It's my age you know. senility is creeping up fast!

SteinarN
09-03-2008, 12:45 PM
Sorry guys', in one of my previous posts I quoted the wrong gas law. It should of course been Daltons' Law of Partial Pressures. I have corrected it to save confusion, but mainly to stop me looking any more of a plonker than I some of you may already think!

It's my age you know. senility is creeping up fast!

I did not notice. I dont even know the name of the law tho i know the implications of it.

Maybe some of our different views comes from different experiences with different systems. My experience is only with smal and moderate size comercial systems.