N.Lewis
26-02-2008, 06:10 PM
Hi guys.
Need to recharge a system, but do not have a vapour charger 'from bottle to guage', bottle has both vapour and liqiud ports, is it o.k to charge from vapour port through suction service valve??

Don't shoot me down if this is a stupid question.
Cheers.

NoNickName
26-02-2008, 06:30 PM
No, it is not ok. Charge from liquid phase to avoid distillation of blend. Use the liquid port in suction valve, making sure that very little liquid is reaching the compressor.

Springbok
26-02-2008, 09:03 PM
Hey N.Lewis...best to charge in the liquid state.Pretty much the same reason as when charging a refrigeration system with R404A.So R407C and R404A are zeotropic refrigerants,which means they are blends.Hope this helps....

nike123
26-02-2008, 09:05 PM
What is size of system?

Brian_UK
26-02-2008, 09:17 PM
Charge in liquid state only.

Throttle back on your manifold valve like a manual expansion valve if charging into a running compressor or until the vacuum has been broken.

N.Lewis
27-02-2008, 09:21 AM
Thanks guy's, i knew it was a dumb question even as i was posting it, but had to make sure, oh well we all have blonde moments...:rolleyes: