View Full Version : Selection of Liquid-Vapor Separators



US Iceman
19-02-2008, 01:58 AM
I thought some of you may be interested in this topic so here are some links for your review.

www.ptac.org/env/dl/envp0102.doc (http://www.ptac.org/env/dl/envp0102.doc)

http://igs.nigc.ir/igs/BANK-MATN/IPS/e-pr-880.pdf

http://www.amistco.com/spanish/tech105.htm

Please remember these are based on conventional practice in the oil & gas industries, but the physics apply to refrigeration also. It is also important to recognize the use of refrigerant or refrigerant and oil may require adjustment of the parameters to meet any requirements you may have.

If you use the above you should proceed with caution if you have not designed separators before.;)

sagittarius
27-02-2008, 04:53 AM
studying......

hendry
29-02-2008, 02:06 PM
very resourceful ...

i feel the basic of such vessel should consider the below few points.

1] sudden surge of liquid returning to the vessel;
2] required vaporation rate;
3] prevent liquid being trasnfer into suction piping
4] other safety issues

hope it helps.

Jacek
17-07-2011, 09:05 AM
I thought some of you may be interested in this topic so here are some links for your review.

www.ptac.org/env/dl/envp0102.doc (http://www.ptac.org/env/dl/envp0102.doc)

http://igs.nigc.ir/igs/BANK-MATN/IPS/e-pr-880.pdf

http://www.amistco.com/spanish/tech105.htm

Please remember these are based on conventional practice in the oil & gas industries, but the physics apply to refrigeration also. It is also important to recognize the use of refrigerant or refrigerant and oil may require adjustment of the parameters to meet any requirements you may have.

If you use the above you should proceed with caution if you have not designed separators before.;)

Hello US Iceman,

As you know, I am investigating pump refrigeration systems. Link http://igs.nigc.ir/igs/BANK-MATN/IPS/e-pr-880.pdf does not work - could you possibly send me this paper?

Thank you in advance.

Jacek

Josip
17-07-2011, 01:25 PM
Hi, Jacek :)


Hello US Iceman,

As you know, I am investigating pump refrigeration systems. Link http://igs.nigc.ir/igs/BANK-MATN/IPS/e-pr-880.pdf does not work - could you possibly send me this paper?

Thank you in advance.

Jacek

Maybe you can try here...

http://igs.nigc.ir/ips/pr/e-pr-880.pdf

or here for some more info

http://igs.nigc.ir/igs/search-out.htm?cx=003832076182005888086%3Axq7-sjin08i&cof=FORID%3A10&ie=UTF-8&q=e-pr-880.pdf&sa=Search#1292

Best regards, Josip :)

TXiceman
24-07-2011, 09:53 PM
My experience with separators designed by oil and gas folks is that they are not well suited to a refrigeration compressor suction. They tend to accept up to 1% liquid droplet carry over and allow for higher pressure drops.

So be very careful using this data.

Ken