PDA

View Full Version : mitsubishi



nikos topts
16-02-2008, 01:27 AM
i finished the installation of a mitsubishi a/c and icame to say hello! in another a/c i had problems with the ground,i had 25 milivolts measured? i think that the compressor doesn"t works good... any suggestions? thanks...

nike123
16-02-2008, 12:53 PM
Is it inverter type of AC?
Did you mean 25mA?

The Viking
17-02-2008, 07:59 PM
If you have any Voltage on the earth terminal, there is a problem with the earth wiring, not necessary with the machinery attached to it......

Springbok
17-02-2008, 09:21 PM
25 millivolts?is the compressor running?if you're not happy with your readings,use a mega meter and trace wires from the mains,you should find th location then.Looks like you enjoy installing them mitsubishis,hey.Fault finding is a brain teaser,aint it?Good luck buddy...

nikos topts
07-04-2008, 12:44 AM
thanks to all!!! but im still trying!!!!!!