View Full Version : Liquid Pumps



bernard
11-02-2008, 10:42 PM
Hi

Visted a site today where they have fitted a invertor on the condenser fans ,lowered the head pressure and fitted a liquid pump.Just looking for views and information on liquid pumps.Are they good ??

Regards Bernard

US Iceman
11-02-2008, 11:18 PM
Hi Bernard,

Any refrigerant pump should be acceptable as long as the pump application parameters are met and the pump is designed for refrigerant service. The system you are describing essentially sounds like a HySave system used in years past for supermarkets and other commercial applications.

Instead of running the system with higher discharge pressures to feed liquid refrigerant to the TXV's, the refrigerant pump simply provides the pressure to push the liquid to the TXV's. Rather straightforward, but...

Refrigerant pumps are notorious for cavitating if the inlet pressure is insufficient.

Chunk
11-02-2008, 11:44 PM
Hi Bernard.the pumps are being used to get head pressures from 200psi to 100psi at night to try and cut down costs.they seem to be working ok as long as the receivers are about 3/4`s full.have`nt had too many problems yet onlystupid alarms when all fans cut out.

Chunk
11-02-2008, 11:52 PM
hysave website is very informative.RE wont let me give url.:)

Josip
11-02-2008, 11:56 PM
Hi, chunky munkey :)


hysave website is very informative.RE wont let me give url.:)

You crossed 15 posts limit now and you can post url ;) try:D

Best regards, Josip :)

Chunk
11-02-2008, 11:59 PM
Thanks Josip now thats 16:)