View Full Version : Fault codes
nigel spring
08-02-2008, 10:32 PM
Hi
Can anyone supply a list of fault codes that includes P5 & P6 on Hitachi Air Con units.
Many thanks Nigel
Latte
08-02-2008, 10:48 PM
Nigel,
If you send me a pm with a fax number i can fax you a list but i have never seen p5 or p6 on hitachi
code 05 is normally a transmission fault with a problem with the power poss incorrect phase problems
code 06 is a voltage problem on the outdoor unit
Hitachi Technical is on 01628 585393
Regards
Fatboy
Inverter man
11-02-2008, 12:08 AM
Nigel, I suspect your unit is a RAS- HVRNE or HRNE.
P6 is a protection code (frost protection),suggesting shortage of refrigerant, blockage etc.
P5 is also a protection code (high discharge temperature) which also suggests shortage of refrigerant or a blockage etc.
Is there a similar adjacent unit? possibly crossed comms cable.
Also if there are adjacent systems and a common H-Link comms is used then the blue dip switches on the relevent I/U O/Us need to be set the same (this is the cycle address or system address).
Good luck
Electrocoolman
11-02-2008, 02:02 AM
Is this what your after:
2005
Josip
11-02-2008, 04:16 AM
Hi, Nigel Spring :)
Welcome to RE forums...maybe to introduce yourself;)
Hi
Can anyone supply a list of fault codes that includes P5 & P6 on Hitachi Air Con units.
Many thanks Nigel
Best regards, Josip :)
Powered by vBulletin® Version 4.2.1 Copyright © 2024 vBulletin Solutions, Inc. All rights reserved.