08-02-2008, 01:41 PM
Can any body give me the
1. comparision chart of the recomended insulation at different temperature.

2. Suitable thickness chart for EPS and PUF.

regards,

narkom
08-02-2008, 07:22 PM
Hi!
You may find the information (including selection program) on

www.armaflex.com/www/armacell/armacell.nsf/ansHTMLSeitenLookUp/India_Frame?OpenDocument

smpsmp45
09-02-2008, 05:44 AM
R u talking about Cold stores? You have to follow Ashrae reco wherein recommended R values are given

rajgulati
11-02-2008, 06:57 AM
I want to know about the thickness required for cold rooms?

Samarjit Sen
11-02-2008, 11:52 AM
Try asking the manufacturers. They would be having it.

smpsmp45
11-02-2008, 01:01 PM
In India, use 125mm Thk PUF / 200 EPS for -25
use 80mm thk puf/ 100mm thk EPS for Chill rooms
& 60mm thk PUF / 80mm EPS for Processing halls.

Again based on the heights, only for structural strength you may have to go in for thicker panels!!!