View Full Version : Evapco Model Number



Gonzalo Arias
11-01-2008, 08:41 PM
Dear Friend:
Does some body can help whith the meaning of a air unit model number?
TFC-33-83-500L
Regards

US Iceman
12-01-2008, 12:03 AM
According to information I have the TFC indicates this coil is a custom unit. My guess on the numbers is this:

33 = square feet of total face area
83 = 8 rows deep, 3 fins per inch
500 = not sure but maybe horsepower of each fan
L = I believe indicates the relative fan section length (lineal space between fans)

That's the best guess I have without calling the factory.

Gonzalo Arias
15-01-2008, 04:43 AM
TK
USIceman, do you know the btu/h per F of TD, and the CFM. I try with factory, but I did not get an answer.
Best Regards

US Iceman
15-01-2008, 04:51 AM
Sorry, I don't have any other information on this.

If the factory will not respond to you rinquiry, then perhpas you could estimate the performance frmo a similar coil with the same dimensions.

For an 8 row deep coil with 3 fins per inch and 33 square feet of face area the BTUH per degree should be similar between coil manufacturers as the heat transfer will not change very much.

Then you could estimate the CFM by multiplying the face area (33 sq. ft.) X 55 feet per minute (for a cooler) or X 800-1000 feet per minute if a freezer.