View Full Version : humidity inside refrigerant circuit


sakly
05-01-2008, 02:09 AM
hi
in a R404A refrigerant circuit , the high rate of humidity 900ppm could induce the formation of ice beans located inside the elbow of evaporator operating at -30°c. ( the phenomenon is called ice bean effect). The situation could lead to create a big force on the elbow and then leakage on the welding.
Do you think this situation is so probable?

nike123
05-01-2008, 02:24 AM
It is more likely that, before that occurs, you end up with capillary tube or TEV blocked by ice.
Correct me if I am getting something wrong here.

The Viking
05-01-2008, 02:55 AM
And with modern refrigerants/oils, an acidic oil mixture that eaten the windings resulting in a burnout.

hendry
09-01-2008, 09:10 AM
yeah .. mos cases, high moisture content in refrigeration piping will cause immediate chockages at high flow low pressure areas ... expansion valves & solenoid valves.

that will be good signs & symptoms for immediate remedies. cheers