Happy Holidays to everyone,I have a question about watercooled condensers on a closed loop system.Whats a good pressure differential across the inlet and outlet? Current numbers are 60 psi inlet/54 psi outlet @66 f. Is there a standard ? Head pressure ok .

750 Valve
20-12-2007, 12:53 PM
2 pass or 4 pass? what mfg? the PD will be affected by the flow rate. You should be able to get the design criteria from the manufacturer

hendry
24-12-2007, 04:17 AM
to us here, not much on standard but reasonable practices.

currently, i'm using the yardstick of 1barG. why?

imagine ... brand new s&t condenser has this value but if aging comes into place & water treatment is not relaible ....

next, i'll also consider the circulating pump's capacity. higher head higher running $.

most cases here, i'll keep the pump head below 5barG. probably 2HP or so.