Hie Gentlemen Of The Trade.

I have problem with a Daikin packaged unit which sucks condensate from the evaporator and spead it arround the supply air plenum. It also fills up the supply air couling. The system is a draw through system. I have tried to increase the air flow so as to increase the evaporator load and temperature in an attempt to run away from the dew point temperature a bit but it looks like it does not work. please give me ideas brothers of the trade

PRESS

RackMechanic
08-12-2007, 07:58 AM
Close fresh air some, clean the evap, and slow down air flow.

philjd26
08-12-2007, 10:43 AM
hi mate,

there should elimator baffles after the dx coil to prevent carry over of condensation which in turn also causes a static ppressure drop.... might wanna see if they are installed..

rgrds phil

Brian_UK
08-12-2007, 11:33 PM
Also check that the drain pipework is clean and properly trapped.

PRESS
09-12-2007, 06:38 AM
hi!

Thanks mate i will make use of your idea.

PRESS
09-12-2007, 06:40 AM
Close fresh air some, clean the evap, and slow down air flow.
Hi there

Thanks for your handy ideas I'll make use of them tommorrow.