View Full Version : Window Heat Pump (A/C)



Rabindra
04-12-2007, 05:03 PM
A new window A/C, (Heat Pump) has unique problem. It operates well on cooling mode but on heating mode (with reverse valve) the heating stops after a while (an hour or so), and the suction pressure equalizes to higher pressure. The heating can be resumed only after the machine is manually switched OFF and turned ON. However same cycle is repeated. I have ruled out moisture in the system, and Reversing valve winding

Please share your experience and help diagnose the fault.

Thanks

EdC
04-12-2007, 06:35 PM
I'd look into the defrost method.

BigJon3475
04-12-2007, 08:06 PM
Sounds like it's not coming out of defrost.

frank
05-12-2007, 12:35 AM
What are the ambient temperatures when you ask it to heat?

Josip
05-12-2007, 01:05 AM
Hi, Frank :)


What are the ambient temperatures when you ask it to heat?

Rabindra is from Nepal and Himalaya is there too....cannot be too warm;) there.....maybe too cold even for Extra Pale Ale.

Best regards, Josip :)

frank
05-12-2007, 02:03 AM
Always start with the basics ;)

Regards Josip

Frank :)